In addition....
Ps.. Well done with all your correct, yet perhaps OTT brackets in your OP
Pps.. I'm not quite sure of your maths though.
Remember the 30% is only taken from the 'excess' current.
e.g if the oven is 4.8kW = 21A, the 30% is only taken on 11A of that as you have already taken off 10A as a fixed amount. So diversity for that one appliance is the first 10A + (30% of 11A) = 13.3A