Discuss Max length of run? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

I think you are trying to do your sums the wrong way around here, You have your panel specs, and your cable distance, what you need to work out is your cable size.

If you do have some losses on the DC side do you see this as a problem?
 
Not my area of expertise, but on your panel spec you should have the voltage,
multiply this by 11 (if you are running on one string) then you will have your DC voltage.

When you say the voltage fluctuates do you mean the AC or DC?
 
have been told by inverter suppliers that i can run 100 meters but i am close to if not over this. what problems could this cause ?
 
Not my area of expertise, but on your panel spec you should have the voltage,
multiply this by 11 (if you are running on one string) then you will have your DC voltage.

When you say the voltage fluctuates do you mean the AC or DC?

not mine either. i can give you max runs on low voltage 230/400 circuits all day long but not sure of my figures on the dc side of things.
 
I would guess that you would have a small drop in performance, if your total panel voltage was say 200VDC and your inverter start up was say 175VDC then it may strugle to start up the inverter, or may not start it up quite as early in the mornings,
That said I am sure you are not cutting things that fine?
What inverter are you using?

Added;You say you have voltage fluctuations, this may cause you a problem, what are they from and to?
Also your AC cable(inverter to supply) needs to be under a 1% loss.
 
really long.

66m before you hit the 1% volt drop threshold, but it's only 1.5% at 100m which can be acceptable in some circumstances.

ps sunny design is your friend for this sort of thing.
 
Just one other point, make sure when you install these DC cables that they are secured and safe, they are high voltage DC and the last thing you want is for them to get chaffed.
 
thanks gavin. what circumstances are these?
where it's not cost effective or practical to move up to 10mm2 cable. TBH I'd only consider it for bigger systems, never go above 6mm2 on something that size, though I guess I've also never gone above a 66m run for a system that size either.
 
ok gavin thanks. its a case of neccesety im afraid the length of run. and in reply to earthstore cables are run on cabletray and in flexible conduit labelled pv every four meters. thanks lads
 
Some of our runs have been nearly 200m round trip on 6mm2, though at nearly 1000V (big strings :) ) Voltage drop is your enemy. As they guys say, Sunny Design is your friend here (it's free) V=IR Voltage Drop = Max Current (Isc) x Resistance (Ohms/m x length in m) Ideally you want as low as possible. At the end of the days it's effiiceincy losses and if cloase to the startup voltage of the inverter will have a bigger impact.
 
bear in mind also that the performance of panels diminishes over time, and also voltage drops with temperature so you need to be comfortably above the start up voltage to make sure the system still works in 10 years time and on a hot day!
 

Reply to Max length of run? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hello, My current 2.5kW Solar pv array is in a less than favourable position, but there is plenty of space to expand the array. I have an...
Replies
2
Views
1K
i want to run a something like a BX cable from a sub panel in my garage through an adjacent crawlspace to a fish tank in a room just the other...
Replies
1
Views
303
Insulation test live to earth = 0.7 ohms. This is a long length of buried swa cable (approx 100m) from mains in to submain. Test done with live...
Replies
35
Views
2K
Hello, Can anyone tell me how many apps (max) a S5-GR3P12K pulls, client claims they need 2 x 32amp TP mcbs, calculations shows it shouldnt be...
Replies
0
Views
478
Good morning all. Before I start I am not an electrician and am relatively new to this topic. Current set up Axpert 5.5 Kw inverter, 7 x 420...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock