This may sound like a daft question but in bs 7671 does it state anywhere in it about max ze values
ie

tncs--0.35
tns--0.80
tt--21

I was jut wondering,I can find max zs but not ze ?????
 
from my tutor at college , but since then ive connected generators which have needed readings of 200-250 ohms to be correct for the rcd used , but to my question is it anywhere in the bs 7671 about zE values ? because I were talking to a contractor on site a few days ago and he were quoting regs to me (ive done and passed my 17th edition) but looking through I can not for the life of me find any values for ze? is this anything to do with esqcr regs ?
 
If you want ze supply figures, ring them they will have that data for all their installations.

in your dreams. most of the time they don't even know what , if any, earthing is present. & @ OP. the 21 ohms you mentioned is nothing to do with TT. it's a figure for DNO earthing upstream of your installation
 
took them 5 months to answer my query as to whether or not PME was available at a location. and that only happened because i spoke to them on another matter.
 
You will also find max ze in GN3.
The max Ze for TT is 21 when DNO supplies earth through PEN conductor.
If it is a client owned TT, anything over 200 Mohms is unstable.
 
As far as Ze is concerned, the fabled values are guidelines only, the DNO's are under no obligation to honour them. You get's what you're given and you put up with it!
 

Reply to Max ze values in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Evening everyone . I was changing a fuse board today . Everything tested out fine and good . Until I measured the Ze which is on a tnc-s system...
Replies
7
Views
883
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
1K
Cable calcs using cable calc app Working out cable size for a workshop. 100m long, 100a supply, mccb 100a zs- 0.23 ohms, in a duct on its own...
Replies
2
Views
1K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock