Yea still trying to find them… will have to calculate using the BS time curve tablesAccording to this table they don't exist!
However, interpolating/scaling between 10A and 15A Type 3 breakers to 13A results in 1.42 ohms.
If they are usual type C (instant trip point = 5-10 * In) then you can calculate Zs for cold testing (assuming ~70C operating, etc) as:The breakers shown in the (blurry) picture seem to be these - ABB 60898 S271 type C, not BS3871 type 3.
There are datasheets for these that include the time/current charts.
I don't know if this helps at all...
They do exist but are an oddity, Memshield 2 had 13A devices but are rare as hens teeth.