Hi everyone, does anyone know or know where I can find max Zs value for 750A BS88 gG fuses. I did a periodic during a shutdown last week an was rushed of my feet. I can`t find anything on the web and can`t get back in to check the manufacturer.
 
as a start. i'd use V/I as in 230/5In which gives a value of 230/3750 = 0.06.
 
On the same topic, anyone know of the max Zs for a 947-2 1250A???? Got a reading of 0.06 due to the sub station being very close but I need to note the Max? Anyone got any tables?
 
On the same topic, anyone know of the max Zs for a 947-2 1250A???? Got a reading of 0.06 due to the sub station being very close but I need to note the Max? Anyone got any tables?

Ey up mate, long time no see!!

Why do you need to note the max Zs? Are you using an NICEIC cert? They are the only ones I know of that require the measured and max values. If it's not for a cert and for some other reason, then I can't help.lol


Jay
 
Ey up mate, long time no see!!

Why do you need to note the max Zs? Are you using an NICEIC cert? They are the only ones I know of that require the measured and max values. If it's not for a cert and for some other reason, then I can't help.lol


Jay

lol, thanks for not helping Jay :rofl:

NAPIT EIC working under a national building company with their own electrical managers/experts. No stone un-turned kind of thing. Need to log everything, half expect them to ask "what is the purity of the steel on the SWA"!!!! All good fun and keeping me on my toes but it is/has been 10 X worst than the 2391 exam.


If your reading this Mr. M W, you said it first... "It has been emotional". Who is buying the late night fish & chips next time??? (private joke for when he aka the guest/member lurker reads this :wink: ). He knows my sense of humor by now, this post will put a smile on his face. Lets see who reads this and/or puts a like on it????
 
What make is the mccb i have some tables

Thank you for your help Flanders. It is Merlin Gerin M12 H1

Hospital 4.jpg

I'll be honest, this is the first time I've had anything to do with a 1250A breaker (information only, no direct testing or involvement of the connections etc... Above my experience and it was not needed). Any tables would be useful.
 
Ey up mate, long time no see!!

Why do you need to note the max Zs? Are you using an NICEIC cert? They are the only ones I know of that require the measured and max values. If it's not for a cert and for some other reason, then I can't help.lol


Jay


The last company I worked for was carrying out PIR's on an aircraft factory, we had a visit from the NICEIC as part of their annual checks. The guy that came admitted that their certs where not designed for more than installations greater than 100A.

That's why the big companies design their own certs for very large installations
 
The last company I worked for was carrying out PIR's on an aircraft factory, we had a visit from the NICEIC as part of their annual checks. The guy that came admitted that their certs where not designed for more than installations greater than 100A.

That's why the big companies design their own certs for very large installations

Cheers Ian, I love that you feel the same about certs above 100A/125A.

Mine are 3 x large(ish) PV installs @ 100Kw+ each. Tapping into and feeding the Grid via the main incoming fuse. This needs to be certificated (AC side) BUT we have Supply and Generation! The standard certs do not account for this form of installation, it is difficult to produce a cert for a 800A, 1000A or 1250A incomer. Schematic diagram needed for each install just to show the experts the layout of the install so everyone can understand it.

Standard certs are rubbish!!!
 
Thank you for your help Flanders. It is Merlin Gerin M12 H1

View attachment 30558

I'll be honest, this is the first time I've had anything to do with a 1250A breaker (information only, no direct testing or involvement of the connections etc... Above my experience and it was not needed). Any tables would be useful.
For a merlin Gerin STR23SE and a C1251 I have 0.02 ohms on my chart but I think you can change the settings on theMCCB to achieve higher values
 
Last edited:

Reply to Max Zs values in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Evening everyone . I was changing a fuse board today . Everything tested out fine and good . Until I measured the Ze which is on a tnc-s system...
Replies
7
Views
955
hello , can anyone reccomend a free download for max zs values for bs 3871 ct breakers please
Replies
2
Views
1K
Hi All, Can anyone help with calculating a Zs value for the fuse described in the title. The fuse sizes in Fig 3A3(c) of the 18th edition wiring...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock