Discuss MAXIMUM Ze at origins of TT, TN-S & TNC-S, in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

M

mgnelec09

Hello there,

I know this may sound like a daft question but I am currently looking at A job where the Ze reading is 0.37 in a distribution board.It looks to be a TNC-S system by checking where the board is fedd from at the mains cut- out, the run from the mains is about 70 to this board and they are wanting to add 3x 63 amp circuits.

Does this reding seem to be Ok? The amount of people who have given me different answers over the phone.

Could someone please clarify Max Ze readings for all 3 systems?


Many Thanks
 
Hello there,

I know this may sound like a daft question but I am currently looking at A job where the Ze reading is 0.37 in a distribution board.It looks to be a TNC-S system by checking where the board is fedd from at the mains cut- out, the run from the mains is about 70 to this board and they are wanting to add 3x 63 amp circuits.

Does this reding seem to be Ok? The amount of people who have given me different answers over the phone.

Could someone please clarify Max Ze readings for all 3 systems?


Many Thanks


TN-CS (PME) 0.35ohms
TNS - 0.8ohms
TT - Dependent on means of earthing and csa normally arround 1667ohms but anything over 200ohms should be investigated. In english its reccomend that its under 200ohms i.e put another stake in thats up to you.
 
it sounds as though you are measuring Ze at a distribution board and not at the origin, also it is allowed for the Ze to be greater than 0.35 ohms but the cut out fuse must be reduced from 100A accordingly
 
yeah, where are you measuring your Ze. it's the Zeat source that's max. 0.35.if you are measuring at a DB 70m? from source, you will have the added res. of the feed cable and that Ze/ should be recordede as Zdb.
 
TN-CS (PME) 0.35ohms
TNS - 0.8ohms
TT - Dependent on means of earthing and csa normally arround 1667ohms but anything over 200ohms should be investigated. In english its reccomend that its under 200ohms i.e put another stake in thats up to you.

Remeber these readings are the maxuimum of the supply authoritys side.
TT from the DNO is 21 ohms which is the resistance of there rod at the transformer. A max of 200 it for the Installation side in a TT system so be carefull.
 
Sorry yes the measurement taken of 0.37Ohms was at the distribution board about 70 metres away from the cut out.

The reading at the cut out/ main incomer was around 0.15 Ohms I think.

Does this mean my 0.37 is ok? as they are asking for another board to be installed aboiut 15 metres away powered from this one?
 
0.37 may be fine depending on the overcurrent device being used.

your ZeD.B is 0.37ohms what is your ZeD.B for the new board going to be? you will need to calculate that as well.Then work out the ZS for the final circuits. whit the Zs values you can select an overcurrent device to use.

remember your correction factors,Volt drop, ect
 
There is no maximum allowed Ze, the values are just guidlines.
Now from the information you have supplied, your Ze is 0.15Ω, and apparently your Zdb is 0.37Ω, is this measurement with or without bonding conductors connected?
Zdb should be measured with the bonding conductors connected.
As for the reading being OK, we would not be able to answer that, as we don't know what has been specified by the designer, nor what the R1 + R2 of any final circuits are or their protective devices.
 
Last edited by a moderator:
This reading is with the bonding conductors in place, nothing has realy been specified as it is a private company who seem a bit gung ho!hence me being a little paranoid about there proposed ideas.

Thanks for your input, much appreciated.
They want everything signed off and certified, which I am qualified to do. But for piece of mind, I just needed a little re assurance.
 

Reply to MAXIMUM Ze at origins of TT, TN-S & TNC-S, in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Evening everyone . I was changing a fuse board today . Everything tested out fine and good . Until I measured the Ze which is on a tnc-s system...
Replies
7
Views
883
Afternoon all, Got a bit of a strange one (by my usual standards anyway). Job is a large barn conversion, done years ago, there's loads of work to...
Replies
6
Views
1K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Hi all, For clarity, I'm not a qualified electrician, but have a reasonable amount of experience as I've done plenty of wiring (signed off by a...
Replies
19
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock