Is there anything that you use at same time as your PC that has stayed plugged in throughout? Monitor(s), Speakers, Printer, Fan, desk light.
Had you not already tried a completely different cable I'd have said the most likely cause was a small L-N fault with the split-con cable that tips the balance when under greater load. (It's very difficult to simultaneously IR test every single N conductor and every single CPC conductor, though you may have tested with clips when they are terminated.)
I don't suppose you want to add a clamp meter to your ever growing tool kit do you? They start at around £30 (screwfix)
It would be very interesting to see the reading of the outgoing live when everything is ostensibly "off" in the sun house.
And also the reading when your PC is fired up and running.
Had you not already tried a completely different cable I'd have said the most likely cause was a small L-N fault with the split-con cable that tips the balance when under greater load. (It's very difficult to simultaneously IR test every single N conductor and every single CPC conductor, though you may have tested with clips when they are terminated.)
I don't suppose you want to add a clamp meter to your ever growing tool kit do you? They start at around £30 (screwfix)
It would be very interesting to see the reading of the outgoing live when everything is ostensibly "off" in the sun house.
And also the reading when your PC is fired up and running.