Can anyone tell me if a MCC panel is covered by BSEN 60294 and therefore is excluded from the scope of bs7671 as far as the scope of any inspection and testing of the fixed wiring for the installation?
Thanks.
 
It is excluded from BS 7671 as it is a product, covered by the Low Voltage Directive and thus a product standard.
However, they would fall under the (BS EN) IEC 61439 series.
Not,
BS EN 60294:2012
Measurement of the dimensions of a cylindrical component with axial terminations
 
It is excluded from BS 7671 as it is a product, covered by the Low Voltage Directive and thus a product standard.
However, they would fall under the (BS EN) IEC 61439 series.
Not,
BS EN 60294:2012
Measurement of the dimensions of a cylindrical component with axial terminations
So for the purpose of inspection and testing, only the wiring supplying the panel is applicable to bs7671 and the associated wiring to motor controls and VSD circuits are excluded from the scope of bs7671 and the fixed wiring testing?
If so then who would a client need to see regarding any inspection and testing of the MCC wiring?
 
You can apply the basics tests, the issue is proving ADS using the normal ‘test and inspection’ methods applied to fixed wiring.

For example, VSD manufactures won’t supply tripping curves but state maximum disconnection times under earth faults.

All you can do is the basics but be aware of applying test voltages to sensitive equipment.
 
Can I ask your definition of MCC?

Is this a custom built control panel full of drives, plc, safety circuit etc?

I believe BS EN 60204 may be the correct regulations in question.
 
Can I ask your definition of MCC?

Is this a custom built control panel full of drives, plc, safety circuit etc?

I believe BS EN 60204 may be the correct regulations in question.
Motor control centre
Contains internal mcbs,fused, variable speed drives, contractors, overload relays and the like for conveyer machines for food packaging etc
 
My first question is who is asking and why, is this a insurance request for a condition report of the installation and/or are they asking for a risk assessment and inspection on the machinery, or are you just querying if its supposed to be included.

It often depends on the type of insurance cover that has raised the request as to what is required to satisfy them.
 
My first question is who is asking and why, is this a insurance request for a condition report of the installation and/or are they asking for a risk assessment and inspection on the machinery, or are you just querying if its supposed to be included.

It often depends on the type of insurance cover that has raised the request as to what is required to satisfy them.
Querying if it’s to be included as the maintenance supervisor of the factory wants a condition report done to the whole site as it’s never had one in its existence (around 20-25 years old).
He was the one who pointed out to me if this should be included in the report and too be honest I wasn’t 100% sure.
Usually my inspection and extent of the testing ends at the supply to say a panel , be it a BMS type or a control panel of a similar description.
Either way he wants some kind of inspection on the MCC panels, so if it’s not a requirement of bs7671 then they won’t be included on my report, it maybe that if it does get inspected then it is separate to that of the site fixed wiring report.
What is to be included is the supply’s to the various isolators to the conveyor machinery such as a label controller, X-ray machine, scales etc.
 
Last edited:
I see, as already mentioned explain to him that your periodic condition report is limited as far as the machine supply only, any inspection and report on the machinery itself would be an independent body if that is not your field, he would then need to decide if he is after a risk assessment and/or condition report on the machines and whether some of this is covered by maintenance teams who may be looking after the machinery.

If he is a maintenance supervisor then can we assume he has a maintenance team who repair and maintain the machinery, there report logs and event/maintenance schedules will be probably what he is after to cover the machines or are the maintenance trying to pass the book because they don't won't the responsibility.
 
I see, as already mentioned explain to him that your periodic condition report is limited as far as the machine supply only, any inspection and report on the machinery itself would be an independent body if that is not your field, he would then need to decide if he is after a risk assessment and/or condition report on the machines and whether some of this is covered by maintenance teams who may be looking after the machinery.

If he is a maintenance supervisor then can we assume he has a maintenance team who repair and maintain the machinery, there report logs and event/maintenance schedules will be probably what he is after to cover the machines or are the maintenance trying to pass the book because they don't won't the responsibility.
The fact the installation has had numerous alterations and additions to the wiring, DB’s piggybacked off other DB’s and the like with no sniff of a minor works or electrical installation certificate tells me all I need to know, that there’s not much maintenance logging or at least not much record keeping going on.
And they say the domestic sector of the industry is bad..........
Thanks for the feedback, much appreciated to all
 
The fact the installation has had numerous alterations and additions to the wiring, DB’s piggybacked off other DB’s and the like with no sniff of a minor works or electrical installation certificate tells me all I need to know, that there’s not much maintenance logging or at least not much record keeping going on.
And they say the domestic sector of the industry is bad..........
Thanks for the feedback, much appreciated to all

I've done many many jobs in food and beverage factories, software mods on existing machines, safety upgrades etc. The overriding common theme is the lack of drawings and the amount of bodges to keep production going.
 
So for the purpose of inspection and testing, only the wiring supplying the panel is applicable to bs7671 and the associated wiring to motor controls and VSD circuits are excluded from the scope of bs7671 and the fixed wiring testing?
If so then who would a client need to see regarding any inspection and testing of the MCC wiring?
That is basically correct.
BS 7671 excludes equipment covered by the machinery directive as this is covered by EN 60204-1.
BS 7671 clause 110.2 xi is relevant.
I don't think your use of the term MCC is suitable for a machine control panel, as an MCC would be something somewhat different, and is a rare item in modern equipment.
What you are looking at is the machinery control panel.
BS 7671 stops at the incoming side of the main machine isolator, you cannot apply BS 7671 past there.
Yes, the equipment needs to be checked and verified as safe, but that needs to be done against the relevant standard i.e. EN 60204-1.
If you are going to do this, then you'll need a copy of 60204-1 & the normalised references, and then be familiar with the requirements, and those that are considered relevant under PUWER.
Also, make sure that you are insured for machinery as utilised in the environment, some electrical contractors policies exclude manufacturing machinery because of the possibility of costs in the event of failure to perform etc.
Oh and don't forget that you will also need to be familiar with the manufacturers instructions for the equipment fitted because these have greater significance in machinery than they do in the 7671 world.
 

Reply to Mcc panels and their Appropriate standard in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good evening! Don’t have a huge deal of experience with fire alarms but having to work on a conventional system at the minute with various...
Replies
8
Views
599
Hello, First of all, thank you in advance for any helpful insights posted in response to my question. I have just moved into a new home. With...
Replies
1
Views
1K
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
On eBay you can find hundreds of Samsung (but also LG, Philips, etc.) Smart TV motherboards (see e.g. here Samsung UN65JU6700FXZA Main Board...
Replies
0
Views
816
The seller is saying they will not upgrade the electric and it is normal to have 100 amps. However the inspector is stating it may trip often and...
Replies
4
Views
824

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock