Hi all,

In general do you size the cable to the MCCB full trip setting rather than the adjustable setting for the load being supplied. In some cases upsizing the cable can be costly even from 320/400. One of the site engineers is adamant that it should be sized for full trip setting.

I'm not sure I agree and have rated the cable for the adjustable setting many times previously. What are the views on this.

Thanks

R
 
The reason for using an adjustable MCCB is often that you need a non-standard protection requirement. Turning down the thermal trip point is the most common option, but you also have short-time trip settings on some and possibly EL trip settings as well. All of those impact on what cable(s) are acceptable.
 

Reply to MCCB Adjustable trip setting - cable rating in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all So had some issues lately related to high current fittings .. dp switches mostly. A number of electric boilers of various ratings .. from...
Replies
24
Views
2K
Hi. I have Metrel MI 3152 multifunctional tester and in the Line, Z auto menu there is a setting for Zlim(Z (LPE),Z (LN)) and it is fixed at...
Replies
11
Views
1K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
I’d like your opinions on a scenario I’ve come across. A certificate was produced which contained errors and while there were still faults on the...
Replies
9
Views
2K
I need to augment the underground supply to remote workshops at my own house. I’m struggling to understand the practical implications of voltage...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock