Have you a wander lead ?
Measure R1, then measure R2 separately and see if there are any discrepancies between the two readings. May find it's only on one of the conductors.
 
I have had a very high Zs with LED lamps in when the R1+R2 was fine.I concluded they must be emitting some noise or waveform.That was with a Megger LTW315.
 
May have a bit of earth leakage ? Or an interconnection somewhere on the circuit.
Try a volt meter on low volts and see if there's a small voltage present.
 
Is the code just err or err79? The latter is to do with electrical noise or harmonics on the circuit. This can happen when there are high frequency fittings or dimable transformers plus noise from other circuits on the cu. I would suggest that you isolate all other circuits and try a single lighting circuit.
 
Yea, batteries ? If they are in good condition,
May be worth trying linking at the at the board then doing R1+R2 and adding to Ze.
Sometimes no trip functions give spurious reading as they "tickle" the RCD so as not to trip.
eh?...
twaddle here.
low current loop works as just that....15mA...so as not to trip the RCD.
before this there was D-loc...this worked by injecting a shot of DC into the RCD before sending through the measuring current...so as to `freeze` the RCD....ineffective on modern RCDs...
 
lean something new everyday, thanks for that ☺️
I just rather the adding the R1+R2 to the Ze. Ive never been a fan of trip lock type of functions personally. Cold/dead testing circuits individually first can elevate errors if some of the circuits are energised.
 
lean something new everyday, thanks for that ☺️
I just rather the adding the R1+R2 to the Ze. Ive never been a fan of trip lock type of functions personally. Cold/dead testing circuits individually first can elevate errors if some of the circuits are energised.
dont understand what you are getting at here.
i think you need to go look at the sequence of tests before posting anything else...
:disappointed:
 
The op is powering up the circuit and testing with the trip function.
He's done his R1,R2.
And he's testing with trip lock now, and getting err,
This is a live test,
I'm not sure if all circuits are on or just the lighting.
People connect all sorts of things to all sorts of circuits, before we get involved with trying to sort out issues. Once live they can play havoc to other circuits. Why would a lighting circuit be any different ?
There's not enough information here for me to give a true diagnosis, just throwing some ideas into post.
I'm not wanting this post end up straying from the original problem into a bicker between two other members,
Just contribute some knowledge instead of picking people up on protocol.
Would you pick members up on spelling if the post were educational ?
 
It is 'noise' on the circuit as I had it a while back a couple of times, once on a lighting circuit with a dimmer on it and once on a boiler circuit, I think I linked through the dimmer and it gave me a reading then, the boiler I was going back next day anyway so tried again and it gave me a reading that time although I had already written down calculation value anyway.
 

Reply to Megger 1553 error, what's the problem? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, looking for some ideas on this. I went to an address on Tuesday following a storm where property has been struck by lightning. When the...
Replies
3
Views
753
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K
My main tester is a Megger MFT1711, which I bought second hand but came with a calibration certificate. Rather than annual calibration, I have a...
Replies
4
Views
3K
Hi Folks, have just finished replacing an old fuseboard with a new rcbo jobby. To say there have been a few surprises would be putting it mildly...
Replies
12
Views
1K
Right, so its been one of those long days. swift breakdown: top floor flat. lighting cable is single cores in a conduit system. was employed to...
Replies
35
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock