Discuss merlin MCCB service/test in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
10
Hi I have a client with a 1000a merlin mccb as their incoming PD from their private transformer.
Previous maintenance spark has claimed its faulty and trips under no load, so they’re leaving the compressors running 24/7, I find this odd but don’t want to mess around too much as if something goes wrong it’ll shut down the entire site (100+ employees)
I have contacted Schneider as they were happy to pay to just replace it as it’s running an entire factory site. There is no direct fit replacement available anymore.
The site actual bought a used one as a back up, anyway is there anywhere that could bench test/service tgis 1000a mccb to ensure it’s working correctly to then swap them Over ?
Thanks Paul
 
Assuming it's a Merlin ACB one of the sites we are on had one of the transformers 800A breakers keep tripping when no where near it's rated current. Had to get a specialist in to modify the transformers busbars so both the 800A ACBs could be replaced with new, current production models.

You would probably have to send it to Schneider to get it tested.
 
Assuming it's a Merlin ACB one of the sites we are on had one of the transformers 800A breakers keep tripping when no where near it's rated current. Had to get a specialist in to modify the transformers busbars so both the 800A ACBs could be replaced with new, current production models.

You would probably have to send it to Schneider to get it tested.
 

Attachments

  • 3C9363F1-0F13-4B39-9978-2E2281C92E86.jpeg
    737.2 KB · Views: 20
I'd go down the route of fitting a brand new product, and get the busbars altered during a planned shutdown. At least then you won't be in this position next year when the elderly replacement is also failing. Having a mechanical or electrical failure of a breaker when you are switching it with such high fault currents available is just not worth the risk.
 
I'd go down the route of fitting a brand new product, and get the busbars altered during a planned shutdown. At least then you won't be in this position next year when the elderly replacement is also failing. Having a mechanical or electrical failure of a breaker when you are switching it with such high fault currents available is just not worth the risk.
That’s a fair point,
I just need to find somewhere that can manufacture the new busbars now !
 

Reply to merlin MCCB service/test in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

C
Next Shoe To Drop: Shoddy Solar Panels From China | Zero Hedge Next Shoe To Drop: Shoddy Solar Panels From China The photovoltaic industry is in...
Replies
7
Views
772
sedgy34
S

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock