Discuss Meter tails no rcd in stud wall in the UK Electrical Forum area at ElectriciansForums.net

newfutile

-
Esteemed
Arms
Reaction score
388
During an EICR meter tails were found entering the cavity and coming down a stud wall to a consumer unit about 5 meters (direct distance) away.
they do have an isolator but no rcd or other protection .

as cables buried in a wall have to have (RCD) Residual Current Device at 30mA and generally tails over 3 meters are not permitted by DNO ,how can this comply?
 
They don't!

And more words
 
Is there no fuse either?

I hate meter tails in wall cavities.
 
20220905_120108.jpg
 
As above I hate meter tails being snaked through a wall cavity or run up inside a stud wall with no way of knowing where they are actually sited

Made even worse if there is no RCD protection
 
Are the tails definitely bare in the stud wall, or is it possible they have mechanical protection, complying with 522.6.204, (which I think would mean no RCD req'd)?

I have come across this a few years back in a new build, when putting up a cabinet in a toilet. The tails were installed in a steel stud wall, and my magnet picked up the mechanical protection. Thinking it was just another steel stud, I tried drilling it for a couple of minutes, before realising something was amiss and checked the other side of the wall to find the CU there!
 
During an EICR meter tails were found entering the cavity and coming down a stud wall to a consumer unit about 5 meters (direct distance) away.
they do have an isolator but no rcd or other protection .

as cables buried in a wall have to have (RCD) Residual Current Device at 30mA and generally tails over 3 meters are not permitted by DNO ,how can this comply?
As @Pretty Mouth has said in his post. I have twice now installed tails like this, both times I have used mechanical protection (3mm steel) which may not be visible without chiselling a bit of the wall out.
 
During an EICR meter tails were found entering the cavity and coming down a stud wall to a consumer unit about 5 meters (direct distance) away.
they do have an isolator but no rcd or other protection .

as cables buried in a wall have to have (RCD) Residual Current Device at 30mA and generally tails over 3 meters are not permitted by DNO ,how can this comply?

Cables buried in a wall don't have to have RCD protection, they can have other forms of protection.

As you are carrying out an EICR it is very difficult to confirm whether or not correct protection has been installed. Examination of cables buried within walls, under floors etc is a standard limitation.

You need to make a judgement call as to whether it is likely to comply or not. When was it installed, what is the general standard of the installation, what records are available?
 
It’s a fairly new build 2017 ,the EIC he left at the property does not mention mechanical protection, also the tails must be 8 -10 meters long

Definitely needs a fuse at source then.
 
It's the greater than 3m length with no upfront protection that does it.

 
I watched that efixx vid, and re-watched it a couple of times, and then had a read through the regs mentioned.

433.3.1(iii), 434.3 (iv), and item (ii) of 434.2.1, these make me think that the tails are not restricted to 3m, as long as they are well protected mechanically, and that the DNO agrees that they are protected by their fuse.

Does anyone know under what circumstances a DNO would agree, or even disagree, to this?
 
I watched that efixx vid, and re-watched it a couple of times, and then had a read through the regs mentioned.

433.3.1(iii), 434.3 (iv), and item (ii) of 434.2.1, these make me think that the tails are not restricted to 3m, as long as they are well protected mechanically, and that the DNO agrees that they are protected by their fuse.

Does anyone know under what circumstances a DNO would agree, or even disagree, to this?

They'll probably never agree to it, certainly not for small supplies.
I've found that DNO's generally allow between 3 and 4 metres of tails maximum.
 

Reply to Meter tails no rcd in stud wall in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
814
Hi all -- full disclosure I am a 'DIY-er' but wanted to post here for greater visibility seeing as I certainly won't be doing this work myself...
Replies
21
Views
4K
Can someone sanity check my thinking please.... An 80 amp PME service head, tails to meter, 25 sq mm tails into an enclosed fused isolator with...
Replies
4
Views
1K
I really hope someone can help me. Last July I got an electricity bill showing an enormous rise in my kwh consumption of about 900% from what it...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock