thanks for all the interesting input and advice, i also put the same question to NICEIC but im less than impressed with the reply:
Good Afternoon,
Thank You For Your Enquiry
Based on the information provided, our guidance is as follows;
There is not a specific regulation within BS7671 which states whether or not supply tails with no RCD protection with a length of run greater than 3metres would result in a satisfactory or unsatisfactory outcome.
Do you feel that there is a safety concern or do you feel that an improvement can be made? Please could you also clarify how the tails have been installed.
Once we get further clarification from yourself than we may be able to assist further with your query.
Regards,
Good Afternoon,
Thank You For Your Enquiry
Based on the information provided, our guidance is as follows;
There is not a specific regulation within BS7671 which states whether or not supply tails with no RCD protection with a length of run greater than 3metres would result in a satisfactory or unsatisfactory outcome.
Do you feel that there is a safety concern or do you feel that an improvement can be made? Please could you also clarify how the tails have been installed.
Once we get further clarification from yourself than we may be able to assist further with your query.