OP
Octopus
It sounds to me that at one of the socket-outlets the CPC and neutral are swopped over.
Possibly but that doesn't explain the end to end readings though!
Discuss metrel mi3000 testing for ze in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
It sounds to me that at one of the socket-outlets the CPC and neutral are swopped over.
I can't see a problem with the end to end readings?
I sometimes have problems, doing Zs tests, if the contact with the probes is not very good.
If your meter has frozen, try removing the batteries, leaving a couple of minutes (have a cup of tea or something) and the replace the baterries and re-try.
If that doesn't work, then you will have to return the unit for repair.
thanks iv tryed doing that and still no joy. i just wanted to make sure that before i send it back that its not something that would void the warrenty. also wheres the thanks buttons im new to this!
Hi kelrich, i have a similar prob with a friends installation, i put the post on yesterday "this is odd". I can get a Zs from a SO, but when i try get a Ze, meter wont test. I have a metrel similar to yours and it has a display giving PD between L & N and L & E prior to test. The readings i get are very odd. Thought it might be leads, but they're ok.
Theres some views on the post that marry up somewhat with lenny's above and others. Av a look.
esc
I have a Metrel MI3100 and a similar thing happened to me today, Ze test with earth conductor disconnected - PD between L-E 210v, PD between N-E 42v, total 252v - Metrel refused to test with error message of unrecognised supply. Reconnected earth conductor and re-tested works fine with sensible reading and PDs 230v and 0v as expected. Did you ever get a conclusive answer as to what was happening in your case?
Are you sayoing you tried the Ze with out connecting the earth lead? It sounds like you did - you need to disconnect the main earth (from the MET or CU) to prevent parrallel paths and at the same time remember to connect the earth lead to the "loose" main earth. obviously you'll have turned off the power to the building first!
I definitely connected all three test leads and in the correct configuration including the green lead to the disconnected earth conductor, so I was happy that I was doing the test correctly for Ze, Tried it several times aswell always the same. Reconnect earth conductor to DB earth bar and test with green croc on earth bar and good reading, but this is obviously not Ze (parallel paths etc..).
Based on similar threads, it just seems to be a common occurance with this family of Metrel testers, I will ring Metrel and see if they have an answer, if I get one I will post it.
cheers
Re-awakening an old thread!
View attachment 12490
Same problem here. This is what my tester gave me when trying to do a Ze on a TT system. Zs readings were fine, and Ze without the earth connected gave a >2000ohm reading. Any suggestions?
Presumably the metrel was connected to the cable going to the spike??
Reply to metrel mi3000 testing for ze in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net