Discuss Micro-inverter install in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Reaction score
0
Hello,

I'm planning a small (500W) install with two panels and a dual micro-inverter (APS YC500i) and was hoping to get some advice.

Before I start, I'm aware that adding a new circuit is notifiable under part P and therefore I will get it inspected as required once installed.

So the question or RCDs has come up a few times but I'm not sure exactly how it applies when using micro inverters. I'm specifically wondering about the use of type B RCDs (DC) and micro-inverters which typically would not have galvanic isolation.

On page 6 of the install manual for the APS YC500i (https://usa.apsystems.com/wp-conten...500i_Installation_UserManual-v1.0-7.20.16.pdf) it states the following which further complicates matters:
An AC GFCI device should not be used to protect the dedicated circuit to the APsystems microinverter even though it is an outside circuit. None of the small GFCI devices (5mA-30 mA) are designed for back feeding and will be damaged if back fed. Also, AC AFCIs have not been evaluated for back feeding and may be damaged if back fed with the output of a PV inverter.

I believe that a lot of solar panel installs include a second consumer unit located in the meter box where the main MCB an extra RCD can be added for the solar panel install. My mains cable run is likely going to be clipped to the external wall up to the roof and as such I believe that the use of an RCD is not required. (The cable will not be buried in a wall or underground) I also believe that armored cable is not required and was therefore planning to use Hituf.

The indoor gateway uses power-line communication to communicate with the inverters, therefore I was going to wire that into the non-RCD protected circuit as the communication will work better when it's not going through the consumer unit. For this, I will use either a specifically marked socket or wire it into a marked fused spur unit.

Can anybody confirm that this would be an acceptable installation in line with the regulations and would pass the part-P inspection ? Is there a better way to install these micro-inverters ? I couldn't find a source for type B RCDs.

Thanks,
-Andrew.
 

Reply to Micro-inverter install in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hello there I have just installed a new Solis S6-GR1P3.6K-M-DC Inverter - this replaced a 10 year old+ Sungrow inverter that failed/out of...
Replies
5
Views
2K
Hello everyone, I'm currently working on a project to upgrade an existing renewable energy system and could really use some expert advice. The...
Replies
0
Views
670
I decided to get solar panels, the inverter instructions say one can use type AC, so the existing 14 x RCBO CU seems OK, may be a good idea to fit...
Replies
4
Views
1K
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
910
Hi all, My 3 month old grid tie inverter has tripped on 3 occasions at startup. Have read plenty of threads here about similar issues but unclear...
Replies
1
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock