Discuss Microwave leakage testing in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Reaction score
95
Hi guys I have been instructed to carry out leakage testing on the 3 microwave we have on site as I am the only person on site with 2377 but I'm unsure if the microwave leakage testing req a different qualification as this wasn't on the course or I'm my notes.
any guidance welcome.
 
If you are referring to "radiation" leakage which was a test required in the 3rd edition Code of Practice, it is no longer required in the 5th edition ISITEE. However, I still carry out this test simply due to the fact that I have a tester as I always did the test in years gone by. Just seems daft not to do it as the leakage tester is in my bag anyway and it takes only a couple of minutes.
 
At the very least check the door's integrity and it closes normally (no odd gaps around the side).

The door need not be in contact, just a small enough gap (as it would have if new / not abused) that the EM energy is contained.
 

Reply to Microwave leakage testing in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Hi, I carry out PAT testing on landlord appliances for letting agents in rented accommodation. Occasionally some of the items I cannot access...
Replies
5
Views
787
I may have posted this before but not sure if it made it in. I want to install an EV Charger in my garage. The panel is two stories up and the...
Replies
0
Views
508
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
2K
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
383
Hi all. I recently failed a section of my AM2E assessment. Passed 7/10 but failed on some silly things I'm confident of correcting second time...
Replies
1
Views
438

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock