- Reaction score
- 7,231
Hi people,
I'm having a brain fart moment. What is the minimum distance between enclosures, with doors that are facing each other?
In EN60204-1:2006+A1:2009 section 11.5 said " In the case where such parts are present on both sides on the access way, the clear width shall be at least 1.5 m."
In EN60204-1:2018 section 11.5 has removed the dimensions for between cabinets. Not sure why.
Ok, so the only dimensions I can find now between enclosures are in BS7671 section 729. Operating And maintenance Gangways. Which says 700mm.
So, my question is, am I missing something? Is there any other reg I'm missed, or are we just going with a distance of 700mm now?
I'm having a brain fart moment. What is the minimum distance between enclosures, with doors that are facing each other?
In EN60204-1:2006+A1:2009 section 11.5 said " In the case where such parts are present on both sides on the access way, the clear width shall be at least 1.5 m."
In EN60204-1:2018 section 11.5 has removed the dimensions for between cabinets. Not sure why.
Ok, so the only dimensions I can find now between enclosures are in BS7671 section 729. Operating And maintenance Gangways. Which says 700mm.
So, my question is, am I missing something? Is there any other reg I'm missed, or are we just going with a distance of 700mm now?