B
bhmike
Just installed 62kW on a roof along with 38kW on ground.
The 62kW feeds 3 X Tri-power 17000TLs Then into a TP&N board via 3 X 40A mcb out through a 300mA incomer.
50mm 4Core sub-main (45 metres long) to a 400A Panel board. The sub-main is protected by a 300mA S-type RCD (on a farm).
The S-Type RCD protecting sub-main trips (not immediately) if more than 2 inverters on. The 300mA RCD on TP&N board is fine.
All RCDs are AC type as SMA say no risk of DC leakage.
What I don't get is why the S type is tripping and not the other.
Probably some highly technical reason for this - any ideas anyone?
The 62kW feeds 3 X Tri-power 17000TLs Then into a TP&N board via 3 X 40A mcb out through a 300mA incomer.
50mm 4Core sub-main (45 metres long) to a 400A Panel board. The sub-main is protected by a 300mA S-type RCD (on a farm).
The S-Type RCD protecting sub-main trips (not immediately) if more than 2 inverters on. The 300mA RCD on TP&N board is fine.
All RCDs are AC type as SMA say no risk of DC leakage.
What I don't get is why the S type is tripping and not the other.
Probably some highly technical reason for this - any ideas anyone?