I have an an electric brake on a three phase motor with the attached wiring schematic which is part of a wine press. At first I thought this was the Wye/Delta wiring layout but I am starting to think this is actualy a low/high voltage schematic but they are using the wye/delta symbols. There is no neutral shown on the schematic for the brake nor is there one in the press itself. I am a bit confused at this point.Brake Tag.jpgBrake Wiring.jpg
 
It is both,
star configuration for 400v (3 phase)
delta for 230v (3 phase)
the brake is not mentioned in your pictures, often the brake is fed from a rectifier off the windings so the brake coil is energised and the brake turned off when the motor is powered and is spring activated when power is released.
 
It is both,
star configuration for 400v (3 phase)
delta for 230v (3 phase)
the brake is not mentioned in your pictures, often the brake is fed from a rectifier off the windings so the brake coil is energised and the brake turned off when the motor is powered and is spring activated when power is released.
I have 208V Three Phase. The brake is wired directly to the terminals inside the motor wiring box. Thanks for the info on the star for higher voltage and delta for lower voltage. That is the answer I was looking for.
 
208v might be a little low for that motor, if it is loaded anywhere near its maximum rating, i would expect it to overheat.
 

Reply to Motor Brake Wiring Issue in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
656
Heeelp! I have an 11kW/21A motor which is attached to a hydraulic power pack. I have replaced the old panels with new, using the same star delta...
Replies
17
Views
2K
I want to check the insulation of the 3-phase 400VAC asynchronous squirrel cage motor. Motor's stator windings are connected in delta. I've read...
Replies
10
Views
2K
Extremely low voltage on 120v line Hi, I’m not an electrician but my home has 20 amp breaker that has only one outdoor outlet on it with a GFCI...
Replies
2
Views
561
Hi, I am trying to wire a two speed switch to a three phase motor. I have continuity checked the switch in both positions 1 - Low and 2 -High (See...
Replies
1
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock