Good evening,

1) Is the motor current on the nameplate always the full load current: the maximum current the motor can draw without there being damage to its winding insulation.

2) Often in motor books, I see the term nominal current? is this the current that the motor draws under normal operating conditions under load?

3) What the the motor rated current? is this the same as the FLC?



Thanks,

Ewan
 
FLC on the plate is the current the motor will draw at rated voltage and frequency, delivering rated output power. Most motor standards require the motor to withstand small intermittent mechanical overloads, and allow for a tolerance on the supply voltage. So under some conditions, the FLC might be exceeded without damage to the motor.

I would read all these terms with similar meaning, although I suppose there might be subtle differences in the definitions according to context and whether any particular standard is being referenced.
 
FLC on the plate is the current the motor will draw at rated voltage and frequency, delivering rated output power. Most motor standards require the motor to withstand small intermittent mechanical overloads, and allow for a tolerance on the supply voltage. So under some conditions, the FLC might be exceeded without damage to the motor.

I would read all these terms with similar meaning, although I suppose there might be subtle differences in the definitions according to context and whether any particular standard is being referenced.
Feeling better Lucien?
 
Not a great day actually Pete but I'll say more about that in the Arms thread!
 

Reply to Motor FLC, Rated current, running current and nominal current. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
555
Hi Guys, Is my understanding of why it is bad for a star/delta motor to be stuck in star correct? 1) Star delta starting is used as a method of...
Replies
14
Views
5K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
I have a pressure washer that I got as part of "a good deal", actually an exceedingly good deal as I later found out. I've had it a while, I guess...
Replies
5
Views
1K
I want to operate 3 lighting set up using metal halide lamps for studio works or cinematic projects in the future. as of now i have got two...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock