DM7.ENG

I have some calculations to do for aproject I’m working on and the more I look in to things the more confused imbecoming.
When I apply the formula I know relatingto motors I don’t get the parameters which are stated on the name plate forexample…..
I have a name plate with the following
Kw 4 4 4 4.4
380 400 415 400
660 690 690
(7.8) 7.63 7.65 8.29
4.5 4.41 4.79
Cosф 0.88 0.85 0.81 0.86
So for example I want to know the current for delta
I = kw/V*PF
I = 4000/√3*380*0.88
I = 6.9A?? Nameplate states 7.8A
Am I missing something obvious?
 
Last edited by a moderator:
The KW is wrong ..If this was a 4444.4 KW motor you would be the first person to ever see one never mind the thing would be bigger than you and at that voltage probably the size of a bus...

You have a Star/Delta motor there
Missing is motor efficiency but your post is misleading and doesn't make sense ...can you post a pic of the rating plate...rather than trying to interpret it.
 
Apologies its suposed to represent 4kW for each set of characteristics vertically and the last set up is 4.4kW


The KW is wrong ..If this was a 4444.4 KW motor you would be the first person to ever see one never mind the thing would be bigger than you and at that voltage probably the size of a bus...

You have a Star/Delta motor there
Missing is motor efficiency but your post is misleading and doesn't make sense ...can you post a pic of the rating plate...rather than trying to interpret it.
 
as DW said. that difference between 6.9A and 7.8A suggests efficiency of 0.88
 
I have some calculations to do for aproject I’m working on and the more I look in to things the more confused imbecoming.
When I apply the formula I know relatingto motors I don’t get the parameters which are stated on the name plate forexample…..
I have a name plate with the following
Kw 4 4 4 4.4

Refers to the mechanical output power of the motor which is how much actual work the motor can do. A motor rated at 4kW does not mean it's electrical consumption is 4 kW, as Darkwood stated this figure is electrically meaningless with taking efficiency into account which is the losses involved in converting Kilowatts of electrical power into Kilowatts of mechanical power.
 

Reply to Motor name plate query in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock