Discuss motor serial connection in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hi.
I found two single phase 110 Vac asynchronous motors (fans) connected in series to a 220 Vac line, something like this:

live 220 Vac ----------- 110 Vac motor -------------- 110 Vac motor ---------------------neutral 220 Vac

Is there any problems with this connection? the motors are working.
Someone can explain to me what happens if one of the motors try to get more current than the other?
Or if there´s an unbalance of any type?

rbarbali
 
In the most general case of a motor (say with a permanent-magnet DC motor) current is proportional to torque, while voltage is proportional to speed. Series connection makes the two currents equal, therefore tends to make the two torques equal but allows the speeds to differ. However, with induction motors the speed is approximately proportional to frequency, so if the load torque/speed curves are similar, both the speeds and torques will be reasonably similar.

Series connection for identical pairs of small axial fans works particularly well because the torque/speed curve of the loads is similar, and the current doesn't vary very much across all working conditions of the motors because of the high leakage reactance. The voltage divides fairly equally even with differing airflows and the speeds are similar.

Most other types of applications cannot use this method of connection because varying load causes the voltage to divide unequally. Some configurations would be completely uncontrollable and unstable. An exception is where separately-excited motors are mechanically coupled together to run at the same speed. The series connection then tends to cause all the motors to deliver the same torque and hence share the load.
 
Thank you Lucien, you're very clear.
In the case of mechanically coupled motors of different power capacities, both motors deliver same power? Let's say we have 2 motors of 10 hp and 15 hp, what happens if the required load is, say 25 hp? the smaller motor can't deliver 12.5 hp, the bigger motor delivers 15 hp? or the smaller motor slows down the entire power, acting like a brake?
 
If the motors are not identical then how the power divides will depend on the torque constants, not on the maximum ratings. If one motor delivers twice as many newton-metres per amp as the other, then it will take 2/3 of the torque load, regardless of whether it is rated to do so. There is no guarantee that one motor would not be overloaded unless designed for this duty.

If they are connected correctly, neither motor will act as a brake because the torques must always be in the same direction (because the currents are). You could get one motor acting as a brake to the other if they were connected in parallel, and had differing speed constants.
 
If the motors are not identical then how the power divides will depend on the torque constants, not on the maximum ratings. If one motor delivers twice as many newton-metres per amp as the other, then it will take 2/3 of the torque load, regardless of whether it is rated to do so. There is no guarantee that one motor would not be overloaded unless designed for this duty.

If they are connected correctly, neither motor will act as a brake because the torques must always be in the same direction (because the currents are). You could get one motor acting as a brake to the other if they were connected in parallel, and had differing speed constants.
Thanks a lot, Lucien!
 
I should add that this is all a simplification based on motors with ideal characteristics. With AC motors, the magnetising and power currents are in quadrature; when connected in series only the vector sum of these is equal, not the individual components of the current. Therefore dissimilar characteristics can cause a phase difference between the motor voltages, further complicating the behaviour. For the two small identical fans things are relatively tame because of the high resistance and this is why it is one of the few situations where such a connection would be considered.
 

Reply to motor serial connection in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I am looking for a connection diagram or sugestions for a 2.2Kw single phase motor to drive a compressor. The spec plate shows that it can be...
Replies
5
Views
763
Hi Forum Members I have a 4 pole single phase 240VAC 315 watt motor from a central heating heating system that I think is bad. It's the room fan...
Replies
18
Views
2K
I want to check the insulation of the 3-phase 400VAC asynchronous squirrel cage motor. Motor's stator windings are connected in delta. I've read...
Replies
10
Views
2K
Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
659
Hi all. Yesterday I wired in my 3 phase compressor to run off our 53kva generator. I just need to know which colour cable is for which phase as...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock