Discuss Moving cooker switch within prescribed zone in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
5
Hi,

With respect to the cooker switch only. If I moved it 400mm to the left by extending the T&E from its original position using crimps, then tile over the original back box, would it satisfy regs by maintaining the modified circuit within the prescribed zone (assuming all other rules are satisfied)?

I’m aware it will create a new zone vertical to the new switch position, and the outlet will be moved to conform. Its just the movement of the cooker switch I need clarity on. (Moving is the only option available, a new chase is not possible).
 

Attachments

  • zone.png
    6.9 KB · Views: 21
If the existing cable runs vertically up or down then you will need to keep the back box and fit a blank plate as there will be no indication there is a cable in the wall......or rip it out and run new cable
 
Only by doing as Markyd says by fitting a blank plate on existing box so that the existing vertical cable run is obvious.
 
If the existing cable runs vertically up or down then you will need to keep the back box and fit a blank plate as there will be no indication there is a cable in the wall......or rip it out and run new cable
Thanks for the response. The existing cooker switch has the outlet beneath and the extractor take off point above (see image). So by moving the cooker switch to the left, I should be able to bury the old backbox without a plate as the vertical zone should still be preserved?
 

Attachments

  • zone.png
    19.9 KB · Views: 13
Still in the zone.

I’d be inclined to make the joint below the worktop, take it to the side then up to new switch.

Then joint is accessible to a point… have to remove cooker, but it’ll be there.

Only good if cable comes from below.
 
Which is fine if they are good ones, fitted with the right tool. I've seen no-name yellows fitted with A.N.Other brand ratchet tool overheat at 30A, but you're probably bored of hearing me spouting about dodgy crimps in fixed wiring.
 
Which is fine if they are good ones, fitted with the right tool. I've seen no-name yellows fitted with A.N.Other brand ratchet tool overheat at 30A, but you're probably bored of hearing me spouting about dodgy crimps in fixed wiring.
No no, carry on.
We all love a good yarn about dodgy crimps in fixed wiring.
We’re all ears. 😁

Someone else shop with A.N Other hardware?
College tutor 30 odd years ago used to shop there…
 

Reply to Moving cooker switch within prescribed zone in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I am seeking help and best practices to achieve below tasks. I am not across regulations hence will appreciate best approach to achieve below...
Replies
11
Views
3K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
912
Rewiring an old farm cottage… every wall brick and previous wiring not done well at all. I can’t locate any of the prescribed zones diagrams on...
Replies
12
Views
2K
(Trying again, as picture didn't post first time) Hi, I'd be very grateful if anyone could help me here. Below, I've pasted a sketch showing how...
Replies
5
Views
1K
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock