Discuss Multi Function Tester with low battery giving very low insulation resistance reading. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
113
I have a Metrel MI3000 MFT. It has given very low insulation resistance readings for a circuit I was testing earlier today (0.001MΩ) between live and earth(!) but the circuit has been working fine and not tripping the MCB (20A, no RCD as it is a pre-17th ed. CU) and I had tested it only a couple of weeks before with the same MFT and got 81MΩ between live and earth. There has been no work done on the property since that test that could have damaged the circuit (owner says he hasn't so much as put up a picture hook). The battery in my MFT was getting quite low and I have previously noticed inconsistent results with a low battery. Has anyone else had any similar experiences or have any idea if I might be thinking along the right lines in thinking the low battery might be giving misleading results. I have arranged to go back and re-test tomorrow, with a charged battery!
 
Re: Multi Function Tester with low battery giving very low insulation resistance read

I have a Metrel MI3000 MFT. It has given very low insulation resistance readings for a circuit I was testing earlier today (0.001MΩ) between live and earth(!) but the circuit has been working fine and not tripping the MCB (20A, no RCD as it is a pre-17th ed. CU) and I had tested it only a couple of weeks before with the same MFT and got 81MΩ between live and earth. There has been no work done on the property since that test that could have damaged the circuit (owner says he hasn't so much as put up a picture hook). The battery in my MFT was getting quite low and I have previously noticed inconsistent results with a low battery. Has anyone else had any similar experiences or have any idea if I might be thinking along the right lines in thinking the low battery might be giving misleading results. I have arranged to go back and re-test tomorrow, with a charged battery!

You've probably answered your own question! ;)
 
Re: Multi Function Tester with low battery giving very low insulation resistance read

^^^^^ As above ^^^^^

Change the battery/ies.............
 
Re: Multi Function Tester with low battery giving very low insulation resistance read

I had Metrel tester and as above low bat inconsistent readings
 
Re: Multi Function Tester with low battery giving very low insulation resistance read

I once stabbed myself in the thigh to see if I would bleed, after attending A & E and getting put right I tried the same thing again and got exactly the same result which surprised me. Any ideas or advice guys. I might post that up on a medical forum, wonder what the response would be
 
Re: Multi Function Tester with low battery giving very low insulation resistance read

I once stabbed myself in the thigh to see if I would bleed, after attending A & E and getting put right I tried the same thing again and got exactly the same result which surprised me. Any ideas or advice guys. I might post that up on a medical forum, wonder what the response would be

It's like Deja Vu Trev!
 
Re: Multi Function Tester with low battery giving very low insulation resistance read

Just out of interest does the Metrel give readings that low on IR testing ??
 
Re: Multi Function Tester with low battery giving very low insulation resistance read

Thanks all - very re-assuring! :)
 
Re: Multi Function Tester with low battery giving very low insulation resistance read

I once stabbed myself in the thigh to see if I would bleed, after attending A & E and getting put right I tried the same thing again and got exactly the same result which surprised me. Any ideas or advice guys. I might post that up on a medical forum, wonder what the response would be

Lol! When it happened previously it was not quite so extreme, and the MFT came with NiMH AA batteries, which as you will know have memory effect so I didn't want to keep topping them up and so reduce their capacity. Point taken though. Looks like I'll have to keep them topped up from now on!
 
Re: Multi Function Tester with low battery giving very low insulation resistance read

Glad you saw the intended funny side mate, a lot don't and take a big girly huff.
 
Re: Multi Function Tester with low battery giving very low insulation resistance read

Thanks all - very re-assuring! :)
Had similar problem with my first torch mate, threw five of the buggers away before I sussed it
too slow
 
Last edited by a moderator:
Re: Multi Function Tester with low battery giving very low insulation resistance read

Just out of interest does the Metrel give readings that low on IR testing ??

Yes, at least mine does, don't know about the other models. Mine will display anything from 0.000MΩ to >1000MΩ. I was quite surprised when I bought it having been trained on Meggers which only show three digits instead of four.
 
Re: Multi Function Tester with low battery giving very low insulation resistance read

Glad you saw the intended funny side mate, a lot don't and take a big girly huff.

Always good to lighten up an at-times stressful job! Take no notice of the huffs!
 
Re: Multi Function Tester with low battery giving very low insulation resistance read

Had similar problem with my first torch mate, threw five of the buggers away before I sussed it

A re-assuring torch? And that's a problem? Or was it a torch with low insulation resistance? Oh of course you mean the batteries lost capacity because of memory effect! :D:44:

I do have a torch which gives inconsistent results - think it's because I've dropped it a few times!
 
Re: Multi Function Tester with low battery giving very low insulation resistance read

Lol! When it happened previously it was not quite so extreme, and the MFT came with NiMH AA batteries, which as you will know have memory effect so I didn't want to keep topping them up and so reduce their capacity. Point taken though. Looks like I'll have to keep them topped up from now on!

I think you are confusing them with Ni-Cads as it's these that have the memory effect.
 
Re: Multi Function Tester with low battery giving very low insulation resistance read

I think you are confusing them with Ni-Cads as it's these that have the memory effect.

Ah - I thought it was both and only Li-ions didn't. Maybe I'll have a read around this...
 
Re: Multi Function Tester with low battery giving very low insulation resistance read

If these MFTs start dishing out dodgy readings on low battery power, maybe they should just down once the batteries reach a certain level.
It'd make sure you've always got a new set to hand, if you were 3/4 through an I&T on a Friday afternoon!
 
Re: Multi Function Tester with low battery giving very low insulation resistance read

If these MFTs start dishing out dodgy readings on low battery power, maybe they should just down once the batteries reach a certain level.
It'd make sure you've always got a new set to hand, if you were 3/4 through an I&T on a Friday afternoon!

Sounds like a good idea!
 

Reply to Multi Function Tester with low battery giving very low insulation resistance reading. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
615
Hi! Some help would be appreciated! I've just moved into new house, wanting to check insulation resestance etc as getting some nuisance...
Replies
2
Views
336
  • Article
Electrical2Go - Megger MFT Deals! Upgrade your toolkit with our exclusive offer! Purchase any of the Megger advanced multifunction testers –...
Replies
0
Views
635
I want to check the insulation of the 3-phase 400VAC asynchronous squirrel cage motor. Motor's stator windings are connected in delta. I've read...
Replies
10
Views
2K
Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock