beaver74

Hi all

I have a customer who want 3 door bells which are the standard ding dong electro magnet type.I have raised the voltage to compensate but can only get 2 to work.
the trany is a 12Vdc 1A
does any one know if the trany ampage is the disiding factor as the resistance to each bell is 5.25 ohms meaning each bell is trying to pull 2.2A from a 12V 1A trany, will a 12V high current out put trany run these bells
or the other idea is to use a higher voltage and place a resister in series with each bell bring voltage down to the rated 9V
any views
 
Hi all

I have a customer who want 3 door bells which are the standard ding dong electro magnet type.I have raised the voltage to compensate but can only get 2 to work.
the trany is a 12Vdc 1A
does any one know if the trany ampage is the disiding factor as the resistance to each bell is 5.25 ohms meaning each bell is trying to pull 2.2A from a 12V 1A trany, will a 12V high current out put trany run these bells
or the other idea is to use a higher voltage and place a resister in series with each bell bring voltage down to the rated 9V
any views

Try wiring in 4mm, to keep resistance down, try and keep away from the resistors, you will never get all 3 to work
 
I was going to suggest fitting electronic chimes but a quick look on the web and all I got were wireless ones with prices to suit. If you can find some wired electronic chimes they may be cheaper than trying to rewire or experimenting with transformers.
 

Reply to multiple door bells in the Australia area at ElectriciansForums.net

Similar Threads

hi every one new build we done about 6 months ago, had a call to say that the door bell does ding but doesnt dong.... called in today, the chime...
Replies
10
Views
3K
A

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock