Hello community, first time post....
I'm currently working on a bathroom renovation, in which I'm installing a 9kW steam generator/boiler. I'm a moderately skilled DIY homeowner (live in the US) and I believe I'm on the right track but would like some verification from someone who is more skilled/experienced.
The generator is a Steamcore SPA II and here are the electrical requirements from the manual:
Electrical requirements:
Ampere Meter
The total connected load should not be more then 80% of the rating of the overcurrent devices.
Type Electrical Supply Electric current (A)
9kW 240V~ (1PH) 37.5
The data provided above are for 240V(1PH) and 208V(3PH). Consult the manufacturer for
three-phased electricity or electric voltage of other specifications. Within the steam generator,
install an independent circuit breaker so as to provide an electricity supply with
overflow protection and electricity leakage protection (ground fault interrupter.)
Based on these requirements, the 48 foot run of wire and some reading on the web, I've determined that 8/3 solid copper core romex should do the trick. Anyone disagree? With regards to the breaker, am I fine with a 40amp breaker? The part of the requirements that state "The total connected load should not be more then 80% of the rating of the overcurrent devices." leads me to believe that it might require a higher amperage breaker?
Thanks in advance!
Jeralmac
P.S. here's the manual in the event I'm missing information:
I'm currently working on a bathroom renovation, in which I'm installing a 9kW steam generator/boiler. I'm a moderately skilled DIY homeowner (live in the US) and I believe I'm on the right track but would like some verification from someone who is more skilled/experienced.
The generator is a Steamcore SPA II and here are the electrical requirements from the manual:
Electrical requirements:
- 1.Test the voltage of electricity supply and make sure steam generator with suitable electric
- voltage is used.
- 2.Insulated copper wire should be used with an anti-heat temperature of 90 and a
- specified voltage of 300V. Refer to national or local electricity consumption code for
- specifications.
- 3.Install an independent circuit breaker between the power supply and the steam
- generator so to provide an electricity supply with overflow protection and electricity
- leakage protection.
Ampere Meter
The total connected load should not be more then 80% of the rating of the overcurrent devices.
Type Electrical Supply Electric current (A)
9kW 240V~ (1PH) 37.5
The data provided above are for 240V(1PH) and 208V(3PH). Consult the manufacturer for
three-phased electricity or electric voltage of other specifications. Within the steam generator,
install an independent circuit breaker so as to provide an electricity supply with
overflow protection and electricity leakage protection (ground fault interrupter.)
Based on these requirements, the 48 foot run of wire and some reading on the web, I've determined that 8/3 solid copper core romex should do the trick. Anyone disagree? With regards to the breaker, am I fine with a 40amp breaker? The part of the requirements that state "The total connected load should not be more then 80% of the rating of the overcurrent devices." leads me to believe that it might require a higher amperage breaker?
Thanks in advance!
Jeralmac
P.S. here's the manual in the event I'm missing information: