Discuss Emergency Generator Wiring in the DIY Electrical Advice area at ElectriciansForums.net

creggh

DIY
Reaction score
0
Before I pay an electrician to come check my work, I thought it worth a post here.

I don't want to pay the cost of a small car for a whole-house generators I hope never to use, and then have to maintain it. A small inverter generator is enough to get by one, I just need it handy and ready. And I need the family to understand how to use it, so trying to manage power through the existing load center is not an attractive option.

So here's the plan:

  1. The 3,500-watt generator lives in an enclosure at the back corner of the property. The generator has a three prong 110 volt RV plug.
  2. When needed, the generator is connected via a RV power cord rated at 30 amps to the house via a 30 amp NEMA L5-30P three-prong locking inlet box.
  3. This box does not connect in any way to the existing house wiring, but rather to a new two-circuit emergency power load center via a few feet of 10-gauge Romex.
  4. The Romex leaving the inlet box and all Romex in and out of the new load center are secured with mechanical wire clamps tight enough to prevent movement of the wire but not so tight as to visibly deform the outer sleeve.
  5. The emergency power load center is bonded (the neutral, ground, earth ground lead, and case are all electrically connected inside the load center and nowhere else). The load center did not come with a ground bar, so this is done simply by connecting all neutrals and all ground wires to the neutral bar and the neutral bar to the case (via the supplied bonding strip and screw).
  6. The earth ground lead, a green insulated 10-gauge solid copper wire made for that purpose, runs out the bottom of the load center through the same clamp as the inlet (10/2) lead, down the stud (this is in an unfinished garage), under the siding and house wrap, and about 18 inches to a new, independent grounding rod.
  7. The grounding rod is a standard 8' copper-clad steel rod driven into the ground until only a couple of inches are exposed, then securely clamped to the striped end of the ground wire. Because it must be installed inside a dog run with a chain-link floor (to prevent digging) a length of PVC plastic pipe is driven into the ground around the rod to prevent it shorting against the chain-link.
  8. Inside the garage, the 10-gauge inlet wire and the ground wire are secured to the stud with wire staples to protext them against snags, even short as they are. I'll probably cover them later with a piece of HDF.
  9. Inside the new load center:
    1. The #10 inlet hot wire (black) connects to the hot lug on one side (feeding one breaker) and a length of black 10-guage wire jumpers from there down and around to the other lug (feeding the other breaker, so that both are bed from the same 30 amp inlet circuit).
    2. The inlet neutral (white) and ground (bare) both connect to the neutral bar to achieve a bond.
    3. The white pigtail from each breaker also connects to the neural bar.
    4. The black and white leads of the 14-gauge Romex emergency branch new circuits enter the load center, are stripped 1/2", and are affixed to the hot and neutral terminals on the breakers as marked.
  10. Secured at least every five feet by a staple, the two 14-gauge emergency branch wires run up the stud and across a ceiling joist to join the bundle of cabling installed by the builder to carry power from the main load center into the house.
  11. From here, the new wires run across all the joists, through the machine cloth rat-barrier, and through the attic over the breezeway into the attic proper. The machine cloth was removed during insulation and is not so tight as to damage the Romex.
  12. After reaching the attic (of our one-story house) the two circuits part ways:
    1. Circuit A is stapled every five feet along a joist, then dogs diagonally before one last staple and a dive into the wall to feed a new emergency outlet box behind the kitchen refrigerator.
    2. Through the same hole, a second length of the same 14-gauge Romex runs up from the same new outlet and across the attic to dive into the wall of the office. This branch too is stapled every 5 feet.
    3. Down in the kitchen, both wires are connected in the usual way. The grounds are twisted together and one is connected to the ground screw. The hot and neutral wires are back wired to the gold and silver terminals respectively. The receptacle is a new 15A, ordinary 110 volt model of the type that lets you push the striped wire in from the back but requires you to tighten the screw to secure it.
    4. The office outlet at the end of the circuit is wired in the same way except there is just the one wire.
    5. Circuit B instead makes a turn after entering the attic, is fished through an inaccessible space, and runs down inside the wall between the living room and the bedroom where it is connected in the same manner to a new outlet box about six feet off the floor in the back of the closet (to feed the wifi) and then through a few more feet to a new outlet box in a cabinet in the living room. No stapled secure this wire because, except for the point where it enters the wall, there is no way anyone can ever reach it without removing the roof.
  13. All four outlets are labeled as emergency power and given red covers.
That's pretty much it. In the event of an outage, someone has to go out and connect the RV inlet and start the generator. Then the frig, the wifi, and whatever else is needed for the particular situation must be plugged into one of the four outlets. It's easier for the family to understand "don't plug in a bunch of stuff you don't need during an emergency" than have them trying to reconfigure the whole house through the main breaker box.

If it makes any difference, I'm in Houston but actually in an unincorporated bubble. As such I probably don't have to, but I'm trying to follow the national electrical code. Anything I'm missing?IMG_20230617_095419293-s.jpgIMG_20230613_113337960-2.jpgIMG_20230617_100005190-2.jpg
 

Reply to Emergency Generator Wiring in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

I bought a new house in Florida in 2022. Today, I went into the attic. I found wiring stapled to studs in a few places, but there are no guard...
Replies
1
Views
276
Recently moved into a house from the 70s. There's no ceiling light in the living room. Assuming the switch for the room was to one of the outlets...
Replies
1
Views
429
Hello. New member here. Electrical enthusiast. I am at a friend's house in the Bahamas and decided to look at the load center in the house, which...
Replies
2
Views
410
I bought this house a couple months ago. It was built in 1952 (same as me) but has been rewired with yellow 12 awg Romex dated 2007. Looks like a...
Replies
7
Views
513
Hi I've been planning to fit an outdoor junction box at the front of my house to hide a large brickwork hole and properly house the wiring...
Replies
9
Views
879

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock