I have a customer that has 3 heating mats under the tile. This was installed a while back and a relay was used. I measured a 21 amp draw for all 3 mats. I installed a new thermostat that is wifi enabled and it worked well for a while. However I am now throwing a code that says that the current draw is to low. The coil is a 30amp 240v with a 120v coil. The issue is that the thermostat will not see the current draw of the relay coil. The thermostat needs to see a draw of at least 0.3a. Does anyone out there know of a relay that will have a coil relay of at least that, if not a little more? I would like to find a single phase 2 pole 240v with 120v coil that draws 0.4 to 0.5a
 
You won't find a relay with an intentionally higher coil current.

Your best bet would probably be to connect a small dummy load in parallel with the coil.
 
have you looked at the instructions for the thermostat?
i am wondering if it is only suitable for direct connection to the load as it uses current monitoring as part of its feedback loop.
 
Yes I have talked to the people at MySa thermostats and you both are correct. They told me that this thermostat was not designed to be used with a relay. They ran all the wiring to a relay in a crawl space. And they ran 10ga 30amp romex to the relay. From the relay coil to the thermostat they ran 14ga wire. Not nearly enough to carry 21 amps. But the work around that they gave me was to take one of the heat mats (7amp's) and run it through the thermostat therefor giving it a load and let the other 14amp's continue through the relay. Sounds like a good idea I will try that when I go back to his house.
 
Yes I have talked to the people at MySa thermostats and you both are correct. They told me that this thermostat was not designed to be used with a relay. They ran all the wiring to a relay in a crawl space. And they ran 10ga 30amp romex to the relay. From the relay coil to the thermostat they ran 14ga wire. Not nearly enough to carry 21 amps. But the work around that they gave me was to take one of the heat mats (7amp's) and run it through the thermostat therefor giving it a load and let the other 14amp's continue through the relay. Sounds like a good idea I will try that when I go back to his house.
That's what I was going to suggest.
 

Reply to Need relay advice for in floor heating in the Electric Underfloor Heating Wiring area at ElectriciansForums.net

Similar Threads

In July I moved into my new home with Schluter DITRA heated floors in the bathroom. The floor quit working in December, and my GC and a rep from...
Replies
0
Views
343
Hello Guys, I was wondering if any of you nice chaps could lend me some advice. So I have an open vented heating system with a 3 port valve...
Replies
11
Views
2K
Hello all, First of all I apologise if this is in the wrong forum, I figured the general forum may be the best bet :) Thank you for taking...
Replies
3
Views
538
Hi all looking for some advice as a non sparky , be gentle :) To be clear I wont be doing the work myself , just want to be better informed. I...
Replies
7
Views
2K
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
996

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock