Hi all,
Customer reports sporadic nuisance tripping of RCD. I cannot reproduce it, or fault anything, except SOMETIMES on EFLI test it trips the RCD (megger mft 1553 'no trip' test).
I'm out of ideas here, can anyone help? This is what I've got:
- TT installation (small domestic);
- 30mA RCCB main switch incomer (Crabtree starbreaker);
- all circuits IR test 8MOhm to L&N-earth;
- RCD testing off load and on load all fine, ramp test 23mA off load 19mA with everything on.
- Ze about 160 ohms down the rod, drops to 12 ohms with all bonding connected.
 
Might need a leakage tester because combined leakage of the circuits maybe occasionally tipping it over the edge which is what your tester maybe doing.
Ramp test with everything on and running 19mA - I've tested loads of RCDs on load like this and never has one tripped out.
I agree the most likely cause at the moment is combined leakage when something starts up, I just haven't been able to reproduce it.
She also says the RCD was 'tripped' after a power cut - I guess indicating that the startup leakage of everything together was >23mA when the power came back in again. But.... I cannot reproduce that either.
 
Think I'm gonna have to just change the RCD for a new one today and see what happens... 'Tis 5 o'clock after all
I'm not convinced it's a faulty RCD though.
Please keep any ideas coming, I'll post if swapping RCD fixes it.
Cheers guys
 
hi weevilward
had a similar issue turned out to be a wine fridge some years ago, TT system everything on one RCD unit. would not be so bad if it was not in the cellar, every time we tested the circuit we unplugged the fridge to plug in lead light, found a problem on a ring short caused by a mouse, repaired tested time I got home phone call gone again, went back showed house keeper readings on meter IR testing circuit all clear.
anyway customer had all CB's replaced with RCBO units for each circuit & when it went again called me before turning on the RCBO, went in new wine fridge 3 months old causing issue. Maytag replaced no questions asked, did not help client with approximately 4 days of work caused by the fridge.
earth leakage meter very good used one of those a few times very helpful if you can turn on appliances whilst watching the readings.

have also had another fault about 10 years ago TT system same again 30ma trip on mains, IR tested whole house after I managed to take out all of the Neon indicated extension leads must have been 20-25 leads in the house, sh..t loads of electronics plugged in. spent all day on it IR tested could not locate, turned system on again plugged in & RCD down after 10-15 seconds, owner well it must be on a circuit I stripped down the conservatory, kitchen, lounge, heating, immersion, shower. each time I turned the system on I used hoover on each socket circuit & did not matter which one, owner did not believe me thought I was having him on that it was sheer over load of the RCD unit (30ma).
mentioned I would change board agreed price as I had already undertaken all of the testing on the whole house in that day & had results, agreed deduction on my days wages against fuse box change picked my money up next day got phone call my mate will change for less than you.
I lost it & called him c...t, told him good luck with testing his f.....king house, as I would not give him my notes as he did not want to pay for them.
 
Is the 8 Mohm insulation test for the installation
Have you tried L+N to earth with all appliances connected

At a guess I would go with Tels suggestion,a appliance problem,fridge,freezer,washer, Cent heat pump or valve maybe

If it was in Wales its almost certainly a outside light filled with some of the perpetual rain we have to contend with :(
 

Reply to Need some ideas - RCD tripping but everything tests fine.... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
823
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
902
Hello - hope someone can advise please. I have a recently purchased second hand Myford lathe which has a 3-phase inverter (Siemens Micromaster...
Replies
11
Views
1K
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock