Discuss Neutral / earth fault in the UK Electrical Forum area at ElectriciansForums.net

had this yesterday on a TN-S. both RCDs failed to trip on test button and with MFT. found the cable responsible and dissed it, both RCDs now tripping fine. further investigation next week as 1. the cable is short and disappears behind meter board. 2. no idea what the cable feeds as nothing seems to have stopped working.
 
had this yesterday on a TN-S. both RCDs failed to trip on test button and with MFT. found the cable responsible and dissed it, both RCDs now tripping fine. further investigation next week as 1. the cable is short and disappears behind meter board. 2. no idea what the cable feeds as nothing seems to have stopped working.
it`l be for a bypass...
 
RCD will only trip if there's current flowing down to earth. If there's no load on the RCD it won't trip. Other option is that it's faulty, if you ramp test it you'll know for sure.
 

Reply to Neutral / earth fault in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
570
Hi all, Hope you're keeping well I'm currently wiring a small commercial premises. 3 phas incoming supply, 16sq cables As it is in an urban...
Replies
3
Views
353
Hi was recently at a property and was installing a Solar PV system. was doing my testing and i came across a weird result when doing the...
Replies
23
Views
3K
Evening all, I had a quick Friday afternoon domestic job that has turned into a PITA and I'd appreciate your help. While adding some new lights...
Replies
10
Views
910
I'm in a questions asking mood tonight. I briefely looked at a job today and I need to recommend a board change but need to justify it. Firstly...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock