Search the forum,

Discuss Neutral-Earth faults- Don't skip the cross-connection checks! Useless socket tester. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

P

Piratepete

Did a CU change recently, replacing a Wylex rewirable.

Gobsmacked to find 3 sockets in one room on the ring with Earth and Neutral swopped.

I suspected something amiss from the results of my initial L+N to E IR test when lots of things were still plugged in.

The L/N or L/E cross-connection continuity test at each socket will reveal this fault, and must be done.

On radial circuits, an R1 + R2 test at each socket will reveal this fault.

However, on powering up I like to do a quick check of every socket with a socket tester.

My socket tester doesn't register this fault. Is there a reasonably priced one on the market which does?

Cheers
 
Re: Neutral-Earth faults- Don't skip the cross-connection checks! Useless socket test

My socket tester doesn't register this fault. Is there a reasonably priced one on the market which does?

Cheers

Of course not... neutral is bonded to earth at the tranformer. In a TNCS system they're connected in the cut out - for all intensive purposes they are the same conductor at the same potential
 
Re: Neutral-Earth faults- Don't skip the cross-connection checks! Useless socket test

Of course not... neutral is bonded to earth at the tranformer. In a TNCS system they're connected in the cut out - for all intensive purposes they are the same conductor at the same potential

Ok! I just thought that there might be one with clever electronics that could spot the difference. My MFT trips the RCD with a loop test on a faultily wired socket but it's hardly appropriate for a quick check!:uhoh2:
 
Re: Neutral-Earth faults- Don't skip the cross-connection checks! Useless socket test

Yup, see that all the time. I had a light fitting a while ago where all the neutrals were in the earth terminal in the ceiling rose and the cpc was in the neutral. The wonders of DIY huh?
 

Reply to Neutral-Earth faults- Don't skip the cross-connection checks! Useless socket tester. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock