Discuss Neutral fault with LED light fixtures in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hi everyone, I'm new to the industry(Qualified a few months ago). I have a client with 6 LED light fixtures on the same circuit/breaker, 3 are working fine and 3 seem to have a neutral fault(230v live to earth,+/-90v neutral to earth and +/-130v live to neutral).
The rest of the installation seems fine(no tripping).
I was just wondering if there is a simple way to locate the fault.
 
client replaced fixtures himself.
That's the most important clue with this fault.

Where are you testing to get the unusal voltages, at the fixture or the Consumer unit?


forgot to mention all lights were working with incandescent bulbs,

Is that the clients opinion or had they tested L-N, L-E, N-E voltages before fitting the LED's?
 
That's the most important clue with this fault.

Where are you testing to get the unusal voltages, at the fixture or the Consumer unit?

"3 are working fine and 3 seem to have a neutral fault(230v live to earth,+/-90v neutral to earth and +/-130v live to neutral)"

Seems as though they've tested voltage at each fitting. I wonder if they've looked for loss of neutral at loop out of #3 or into #4.

I'd be amazed if homeowner isn't responsible for this fault, by either pulling neutral out when changing lamps or re-terminating on its sheath.
 
Last edited:

Reply to Neutral fault with LED light fixtures in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
625
I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
446
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hello all- I hope this is the right place to ask this question. A few weeks ago the LED lights in the kitchen started flickering intermittently...
Replies
2
Views
695
I installed these round light fixtures in my office 23 years ago. After a few years the circular flourescent tubes went out and I replaced them...
Replies
0
Views
700

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock