Never done a s plan. Stuggling

Discuss Never done a s plan. Stuggling in the UK Electrical Forum area at ElectriciansForums.net

M

Mike Blair

I have never wired an s plan so struggling lol


I have a heatmiser uh4 underfloor heating controlers inhave one on each floor basement ground first n second.

I have a megaflo eco 250 on the first floor

And a boiler on the basement forgot the name i will update

I have no idea how to connect it. Il upload some pictures soon

Any advice in the mean time
 
As Davesparks has pointed out the terminal box on the cylinder with the strip of connectors has connections for the immersion and connections for the cylinder thermostat.

From left to right terminal 1 is common, terminal 2 breaks when temp rises above set point, terminal 3 makes when temp rises above set point, terminal 4 live immersion, terminal 5 neutral immersion and 6th terminal earth.

Immersion feed from double pole switch connects to terminals 4,5 and 6

Cylinder thermostat connects to terminal 1,2 and cpc in 6

2 connects to the brown of the hot water valve and an 1 connects to the terminal of the hot water valve connection in the UH4 where the rest of the hot water valve connections are terminated The heatmiser UH4 wiring diagram shows the connection of the valve.
 
Got to say that is a very cool and generous thing for Leesparkykent to do. After all the rubbish (politics and hate) I have heard and witnessed over the last few weeks it is nice and refreshing to see guys going out of their way to help each other out, Think the day should end in the pub if you are not driving.
 

Reply to Never done a s plan. Stuggling in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top