Discuss New kitchen install over existing wet underfloor heating in the Electric Underfloor Heating Wiring area at ElectriciansForums.net

megzaz

DIY
Reaction score
0
Hi,

I'm getting renovations done to my home, including an existing extension which already has wet underfloor heating. We are moving a kitchen to this area from another room and plan an island with induction hob.

We've just been told that it wont be possible to fit a hob on the island without losing the use of the underfloor heating. Does anyone have any experience of working around existing underfloor heating and how difficult / expensive it would be?

Thanks in advance!
Megan
 
TL;DR
Hob on island over existing wet underfloor heating?
It all depends on what type of floor you have and which way they lay the pipes. It could be concrete then insulation then pipes and approx 70mm of screed in which case there could be enough to chase for cable. You could also hire experienced thermographer and he/she could find a safe route between pipes, but that would depend on how the pipes has been arranged.
 
You’ll have wasted heat under the kitchen units… and don’t try fixing anything the floor.

Yes you could cut a chase between the rows of pipes, but it’s risky.
The thermal camera is a good idea.
The pipes could only be 100mm apart.
 
I don’t imagine running an electrical cable in a heated floor is a fantastic idea, how do we rate the cable that need to be used, I would look for an alternative solution
 
I don’t imagine running an electrical cable in a heated floor is a fantastic idea, how do we rate the cable that need to be used, I would look for an alternative solution

No running it in the heated floor is not sensible but normally you would install the cables on the concrete below the insulation layer so they are protected from the heat.
 
You’ll have wasted heat under the kitchen units
That's not really a problem as it's a constant temperature system - not constant power. So while things will be warmer underneath units, the actual power will be minimal.
I don’t imagine running an electrical cable in a heated floor is a fantastic idea, how do we rate the cable that need to be used, I would look for an alternative solution
How would you rate a cable for any other installation that didn't run at 20˚C ambient ? Typically a wet UFH will be limited, both by a thermostatic valve, and in my brother's place an over-temp cutout on the manifold as well.
So realistically, your cable is going to be at an ambient of around 30-35˚C max, which from a very vague recollection is going to require a derating factor in the order of 0.5.

As others have already pointed out, the "tricky bit" will be digging a chase without damaging the pipe - though in-situ pipe repairs are possible if it's needed. However, I strongly suspect that almost all kitchen fitters and electricians will consider this in the "far too difficult, just tell the customer it's impossible" category. It's not, just very difficult - they won't be able to just whizz the chase cutter across as many will have become used to.
At one time, digging out chases was something given to the apprentice or junior (going back even further, drilling holes to fix sockets/switches with the "revolutionary" Rawl drill was also given to the lowest in the pecking order) - and for good reason. These days the apprentice or junior seems to have been replaced with the chase cutter - not that I'd have given this job to an apprentice (except perhaps the bulk bits between, and not close to, the pipes) ...

So first thing to do will be to locate the pipes. When I helped a mate out with renovations a few years back, I took a load of photos, including with measuring tapes in place, which I gave to him so that in the future there needn't be any guesswork as to where the wires are under his bathroom floor. I rather suspect that few installers do that, and if they do, the house owner doesn't realise their value and they don't get passed on to the next owner. Luckily when I bought our current house, the previous owner still had a "partial" set of architect and structural engineer drawings - though sometimes, on the "ignorance is bliss" approach, I sometimes think I might have been better without 😬
As mentioned above, a half-decent thermal IR camera should be able to locate the pipes. You'll need to let the slab cool for a while (sticks finger in air and guess, perhaps several days). After that, you turn on the heating full whack and watch the camera. It may take minutes, it may take hours, depending how deep the pipes are and floor construction - but you should be able to see hot lines appear and mark them on the floor.

When you have a good idea of pipe location, and with the acceptance that there's no guarantee you won't damage any pipes, you start chasing by hand - carefully. If you are quite sure where the pipes are then you can knock out in between them quite quickly, but as you get closer you need to be more and more careful.
At first, you'll be working as if the next blow in the chisel could put it through a pipe - and this could go on for a while as you won't know how deep they are. But you may get some clues while doing between the pipes - e.g. finding the top of the insulation or boundary between main raft and screed. Once you've found the first pipe, you'll have a better idea - but you can't assume they'll all be at the same depth.
This probably sounds time consuming - it will be 😱 And the bill will match that unless you elect to do the long slow hours yourself.

Oh yes, it may well be a good idea to isolate the UFH while you are doing this 🙄

Having found the pipes, you then decide whether to take the cable over the top of them (if they are deep), or (also really carefully) tunnel under them if they are shallow.

There is the option of running a conduit into which a cable is drawn, or just concreting the cable in place. There are pros and cons both ways. I'm a conduit whenever I can sort of person as I like to be able to replace cables if they get damaged or requirements change. I'm just finishing up in our lounge, and the previous owner who built the extension just clipped the cables to the walls and plastered over them. That meant digging out what seemed like miles of chase to free up cables I wanted to move 🤬 But you need more space, and it slightly lowers the current carrying capacity of the cable.

And if you get all this work done, consider if there's anything else you might want at that island - you've just done all the hard work, right ? Though I would point out that a drain for a sink will be impossible (or at least very impractical) given that there are so many other constraints with a drain.

And have the UFH pipes well pressure tested before reinstating the floor - if there's a weak spot you want to know about it now while it's relatively easy to deal with ...

So, in summary :
Contrary to what you have been told, it may well be possible to have both your island and keep the UFH.
Not a lot of trades will care enough to even consider that it's possible.
It's not going to be cheap, and it's not going to be quick.
You may have to "positively rebut" a number of explanations why it's "impossible". Most of these will translate into "too much hassle and I don't want to do it" - or worse, "I'm rubbish and my job and I can't do it" (in which case, find someone who can).
You'll probably need several trades - especially I wouldn't allow most plumbers or kitchen fitters anywhere near electrics.

That probably raises more questions than it answers ...

Simon
 
And another though on cable derating ...
Normally the higher rating of a 90°C cable can only be used with higher rated accessories. But in this case, the concern is a mid section of cable.
So using 90°C rated cable would give additional headroom. If the floor reaches (say) 40° then I seriously doubt someone will still be stood on it using a hob ...
 
A bit crude but I'll throw it out there.
I have seen it done with some success before, If you allow the exposed screed to cool right down then soak it in water for a while so it goes damp, then immediately whack on the UFH full throttle you sometimes get slightly dryer lines forming initially immediately above the buried pipes, before the heat eventually disperses. As I said though, this is only a crude method and doesn't always work, also depends on the depth and spacings of the pipes etc...
 
Screed will be 100mm thick, and UFH pipes will be at the base of that and 15mm diameter. So no reason why you can chase down 50 - 70mm or so to accommodate new cables. Also with use of a thermal camera you may well be able to get between the UFH pipes.
 
Screed will be 100mm thick, and UFH pipes will be at the base of that and 15mm diameter. So no reason why you can chase down 50 - 70mm or so to accommodate new cables.
I've fitted plenty of wet UFH systems, and the screed is normally 60 - 65mm thick. The pipes are on the surface of this, so nominally the top of the pipes is about 45 - 50mm below the surface. I leave the pipes all carefully clipped down on the insulation, but after the builder's labourers have clomped all over in their size 12s with barrow loads of screed, I wouldn't guarantee anything more than 30mm.
I've also fitted UFH under chipboard floors, and in these cases the pipes are immediately under the board.
It would be a good idea to go for the kind of kitchen units that sits on exposed decorative legs, rather than those with kickboards.
 
Unless you have first hand knowledge of the specific building being discussed here how can you be so certain of this?
Good point...just going by personal experience on best practice having been through some renovation projects. However, thickness doesnt really matter as even if its as thin as, say, 50mm, with use of a thermal camera and careful grinding, it will be possible to create a channel to take some low profile conduit.
 
Good point...just going by personal experience on best practice having been through some renovation projects. However, thickness doesnt really matter as even if its as thin as, say, 50mm, with use of a thermal camera and careful grinding, it will be possible to create a channel to take some low profile conduit.

But you want to avoid having the cables in the heated screed otherwise you end up with much bigger cables.
 
Have you asked the person who did the underfloor heating if they have a picture of it before screeding?
It is a common think they do for multiple reasons. This would give you reference points.
I wouldn't vory about heat much as any competent sparky would figure that-one easily out...
 

Reply to New kitchen install over existing wet underfloor heating in the Electric Underfloor Heating Wiring area at ElectriciansForums.net

Similar Threads

My mother moved into her three bed home in 1960 and it had underfloor heating in the living room. I remember we used it when I was growing up in...
Replies
5
Views
2K
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
805
Morning all, I'm about to embark on some home renovation and the kitchen is the first target. We are looking at making it bigger, all in the room...
Replies
37
Views
10K
Hi. We have moved into a new build house in Feb this year that has infrared underfloor heating and an economy 7 tariff. For info we also have...
Replies
5
Views
2K
Hi all looking for some advice as a non sparky , be gentle :) To be clear I wont be doing the work myself , just want to be better informed. I...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock