Discuss New Lathe in the Workshop in the Commercial Electrical Advice area at ElectriciansForums.net

Reaction score
76
Over the summer we had some single phase workshop gear removed, and in it's place was delivered a second-hand 3-phase lathe. At first I was going to drop in a new circuit, as naturally, the single-phase circuit that exists is useless. However, this new lathe is going right next to another lathe we have that is fed off a C16 MCB. This circuit terminates in a MEM Exel 20A switch disconnector, which the current lathe ties in to.

The current lathe is 5.1A and the new lathe is around a couple amps from memory - can anyone see an issue with dropping the new lathe in to the same switch disconnector (except that to isolate one for maintenance means to isolate them both - not an issue)?

Thanks,
 
Over the summer we had some single phase workshop gear removed, and in it's place was delivered a second-hand 3-phase lathe. At first I was going to drop in a new circuit, as naturally, the single-phase circuit that exists is useless. However, this new lathe is going right next to another lathe we have that is fed off a C16 MCB. This circuit terminates in a MEM Exel 20A switch disconnector, which the current lathe ties in to.

The current lathe is 5.1A and the new lathe is around a couple amps from memory - can anyone see an issue with dropping the new lathe in to the same switch disconnector (except that to isolate one for maintenance means to isolate them both - not an issue)?

Thanks,
why not add a 2nd isolator on the same circuit., parallel with exsting iso.?
 
Was common practice in the 70s and 80s to parallel two or three machines to one circuit, rarely see it now but I don't see a problem.
 

Reply to New Lathe in the Workshop in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

So far I have never had to deal with a new supply but a possible site we are looking at will need some major changes and so I wondered if folks...
Replies
2
Views
706
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hi all, first post so go easy! This is for people who are looking for more info on the course and exams and is from my experience of doing the...
Replies
1
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock