Discuss New outlet does not have enough power in the UK Electrical Forum area at ElectriciansForums.net

Nitzey

DIY
Reaction score
3
I installed a new GFI outlet in our bathroom for our new electric toilet. To do this I cut wires to the exhaust fan and added new wires to the new outlet. The three wires, from the breaker, to the exhaust fan, to the new outlet, were joined together with wire nuts. #12 gage wire. When all the functions on the new toilet did not work, I called the manufacturer. He told me to try a hair dryer in the new outlet and sure enough it did not work. A device with a light load, a small fan, works fine. Interesting if I turn on the exhaust fan, the fan turns off. Also, the new GFI outlet reads 120V but zero if the exhaust fan is on. I am going to have to tear the wall apart after having painstakingly repaired it. I don't quite understand all this.
 
I installed a new GFI outlet in our bathroom for our new electric toilet. To do this I cut wires to the exhaust fan and added new wires to the new outlet. The three wires, from the breaker, to the exhaust fan, to the new outlet, were joined together with wire nuts. #12 gage wire. When all the functions on the new toilet did not work, I called the manufacturer. He told me to try a hair dryer in the new outlet and sure enough it did not work. A device with a light load, a small fan, works fine. Interesting if I turn on the exhaust fan, the fan turns off. Also, the new GFI outlet reads 120V but zero if the exhaust fan is on. I am going to have to tear the wall apart after having painstakingly repaired it. I don't quite understand all this.
You are not going to have to tear your wall down. It sounds to me like you have crossed some wiring. First off you stated that you pulled a cable from the fan/ light for a GFCI receptacle. All the blacks and whites at the fan should have stayed together and then tie your new cable with them also. The GFCI will not work unless you hook the wires up to the line side of the GFCI. Could you please take some pictures of your receptacle and fan wiring
 
You are not going to have to tear your wall down. It sounds to me like you have crossed some wiring. First off you stated that you pulled a cable from the fan/ light for a GFCI receptacle. All the blacks and whites at the fan should have stayed together and then tie your new cable with them also. The GFCI will not work unless you hook the wires up to the line side of the GFCI. Could you please take some pictures of your receptacle and fan wiring
 

Attachments

  • 94B89DB7-36DB-4D34-B35E-6B61B5BD5D1B.jpeg
    317.7 KB · Views: 12
  • 1C92B576-EED6-434D-90E1-F2580A92FF7E.jpeg
    329.3 KB · Views: 13
  • FA3CC42A-3ACA-41C8-9F8F-BEB9EC87053C.jpeg
    337.5 KB · Views: 14
  • 1F788D2E-8E4D-4063-9426-F45E311601E7.jpeg
    327.7 KB · Views: 16
  • 63F438CB-137D-4C96-A565-F8D42FB30A03.jpeg
    332.7 KB · Views: 13
I installed a new GFI outlet in our bathroom for our new electric toilet. To do this I cut wires to the exhaust fan and added new wires to the new outlet. The three wires, from the breaker, to the exhaust fan, to the new outlet, were joined together with wire nuts. #12 gage wire. When all the functions on the new toilet did not work, I called the manufacturer. He told me to try a hair dryer in the new outlet and sure enough it did not work. A device with a light load, a small fan, works fine. Interesting if I turn on the exhaust fan, the fan turns off. Also, the new GFI outlet reads 120V but zero if the exhaust fan is on. I am going to have to tear the wall apart after having painstakingly repaired it. I don't quite understand all this.
. You shouldn’t have to wrap wires around the screws. and are you sure that you wired your GFCI on the line side and not the load. It’s stamped on the back
 
. You shouldn’t have to wrap wires around the screws. and are you sure that you wired your GFCI on the line side and not the load. It’s stamped on the back
I am sick of the hassle of wrapping wires around the screws and so installed spade terminals. Just now. I think the wires were connected properly to the line side. Used Ancor terminals; they are excellent.
 

Attachments

  • 884ECAC2-08EA-4C07-97FE-ECAB944BD5A7.jpeg
    281.7 KB · Views: 10
  • 33703415-E880-461F-B701-C99D69FFB842.jpeg
    427.8 KB · Views: 9
  • 7C65E29D-AA3A-4B1E-897E-C961E5CC2598.jpeg
    257 KB · Views: 12
  • IMG_3047.MOV
    984.7 KB
I am sick of the hassle of wrapping wires around the screws and so installed spade terminals. Just now. I think the wires were connected properly to the line side. Used Ancor terminals; they are excellent.
I have discovered the problem and fixed it. Although the wiring is simple I had managed to screw it up. But now repaired and everything works great.
 

Reply to New outlet does not have enough power in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm looking to install a new bathroom extractor fan in my bathroom as I have a windowless bathroom and the current one I have installed in...
Replies
13
Views
690
Hi all. I have a power outlet that has no power coming to it. The breakers all appear to be untripped (I turned them off & on again to make...
Replies
2
Views
778
Mobile home outdoor power supply is a pedestal that power to the mobile home plugs in much like an RV. The main power supply into the mobile home...
Replies
6
Views
854
Hi, have an old bathroom fan. Which has two wires the black and red (line and neutral). The fan has no isolator switch and was powered when the...
Replies
3
Views
698
Hi, I am installing a new bathroom fan. We had an electrician who ran 14/3 into a junction box. The black feeds a led light and the red was...
Replies
1
Views
700

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock