Discuss New Socket Protection Question in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
I have to install 2 new sockets into a garage, but unfortunately the consumer unit has all spaces allocated. One of the circuits has a 40Amp circuit breaker that is feeding a CU out into a summerhouse.

The maximum load in the summerhouse would be around 10Amps with the summerhouse heater that is not on regularly but is taking up most of the load. Would it be easier to change the 40Amp circuit breaker out to a 20Amp, wire in the 2 new garage sockets in 2.5mm twin and earth (ran in plastic conduit), therefore creating 2 radials out from the 20Amp MCB?

Or any other guidance appreciated.
 
Not a good idea IMHO - as these are totally separate areas they should have separate OCPD so that a problem in one area does not involve isolating the other. Also reasonable to think that a 13A load may be used in the garage, which with the 10A in the summerhouse would be over the 20A.
 
What circuits does the existing board have?
It has mostly separate shower, cooker, smoke alarm, upstairs/downstairs 6Amp Lighting and 32Amp protected ring main for upstairs/downstairs.

Just going to go for installing a new CU. Kill the board supply and throw in some 25mm singles from dead side of CU isolator into a combined MCB/RCD unit and take new radial circuit off that, sticker the board up with switch off mains before removing cover.
 
The garage is wired up for radial and want to keep it that way as the 20mm conduit and the amount of bends in this would be a PITA to feed 2No. twin and earths down. Plus dont think its best practice to shove 3 cables into the ring main circuit breakers.
 
Last edited:

Reply to New Socket Protection Question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
906
Hi all Now being upfront I am not a sparks. I am about to have some work done by a friend (certified) and as he is doing me a favour I want to as...
Replies
5
Views
2K
I may have posted this before but not sure if it made it in. I want to install an EV Charger in my garage. The panel is two stories up and the...
Replies
0
Views
501
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
895

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock