is that due to global warming affecting the values due to higher ambient temperatures? :ack2: or is it the polar icecaps melting and relocating true north?They are all 5% lower than the previous figures.
is that due to global warming affecting the values due to higher ambient temperatures? :ack2: or is it the polar icecaps melting and relocating true north?
is that due to global warming affecting the values due to higher ambient temperatures? :ack2: or is it the polar icecaps melting and relocating true north?
gee Thanks I think.....
OK, to be more clear, has anyone seen a nice printable table in pdf format.
(yes I have new books, but I want to print a table to stick on the wall by my desk to replace the old one)
#18 are you sure about 32amp
if the table is correct in the above post, nappit at 80% = 1.10 ZS for 0.4 60898 or 61009
if that is correct then 1.10 x 1.2 = 1.32 not 1.37 as in post 18.
Unsure now
#18 are you sure about 32amp
if the table is correct in the above post, nappit at 80% = 1.10 ZS for 0.4 60898 or 61009
if that is correct then 1.10 x 1.2 = 1.32 not 1.37 as in post 18.
Unsure now
#18 are you sure about 32amp
if the table is correct in the above post, nappit at 80% = 1.10 ZS for 0.4 60898 or 61009
if that is correct then 1.10 x 1.2 = 1.32 not 1.37 as in post 18.
Unsure now
Hi there
ok so you don't like the way I got to the figure fair enough, but as you have more knowledge than me answer these questions then
what are we proving with max Zs ?
What realtionship does this have with say a 32A breaker 60898 type B
there must be a relationship between breaker & the value otherwise there would be no value so what is it
so so if you have the above how do you get to 100% in the book
show me the math
forget my second Gn3 part although math might not be how you would do it I still get the correct answer
so show me your math just looking at how you get the figure in the book there has to be a reason ie like ohms law you can't change it it is a fact
Not getting the hump I am asking you to prove what the book says is correct where did the value come from as my formula may not or maybe correct I still get to the correct answer I already know the relationship between the value & the breaker.
I am asking you to prove it after all this is a forum which is to promote discussion & answers, if I am wrong I am happy to admit it, but the formula is givin the correct answer at the end how I get there I have shown without the use of the book, I am just asking you to prove how they get the answer or the relationship between the answer & the breaker sorry of I come across rude or if I have the hump I have not just looking to check the math
What a bloody convoluted exercise the IET have made of Max Zs values. Think i'll stick with values that has been in use from time immemorial and has worked perfectly well during that time....
That doesn't make sense Eng
Unless you can remember every max Zs for every device you are going to have to look them up.
So are you going to keep a copy of the old regs just to use the Zs tables?
Or are you just not going to get the new book and carry on working to the bgb?
Max ZS for any type B breaker 60898 or 61009
Type B = 5 x
at present using 230volts before the change to 220volts
lets use 32A type B breaker for this example
32A x 5 = 160A
160 A is fault current that will trigger breaker
we have our 160A now what
230v our supply voltage Uo
230/160 = 1.43 this is 100% value for ZS
1.43 x0.8 is our rule of thumb
1.43 x 0.8 = 1.15 corrected ZS actually book states 1.16 table B6 OSG P119 green book
so now for our new GN3
32A x 5 =160A
supply Uo 220v
220/160A =1.37 max ZS
corrected value = 1.37 x 0.8 = 1.1 ohms
Using green book values for C & D
type C use x 10 32 x10 = 320 230/320 = 0.78175 0.78175 x 0.8 = 0.575 rounded up = 0.58
type D use x 20 32 x 20 = 640 230/640 = 0.359375 0.359375 x 0.8 = 0.2875 rounded up = 0.29
dont need the book as the sum won't change just one value which would be 230 going to 220v. the figure gives 100% but just x 0.8 to give the rule of thumb
i have never measured 230v though and thats what i was getting at, i have measured 232 or 226v etc so you do need to work it out each time based on your reading.nominal voltage hasn't changed you are correct but the Cmin factor is applied to the nominal voltage when calculating the maximum zs of an OCPD to counter in the permitted tolerance of +10%/-6% in voltage variations. That is where GB kayak has got 218.5 volts from. you would of thought they would of given us a correction factor of 0.94 instead of 0.95 considering the minimum permitted voltage range is 216.2 volts (-6%) but the powers that be deemed 0.94 to be un realistic (another fine contradiction might I add).
i have never measured 230v though and thats what i was getting at, i have measured 232 or 226v etc so you do need to work it out each time based on your reading.
i have never measured 230v though and thats what i was getting at, i have measured 232 or 226v etc so you do need to work it out each time based on your reading.
yeah i know, i took the picture with my phone using my own regs bookThe calculation is provided on the right hand side of the picture you have posted.
yeah i know, i took the picture with my phone using my own regs book
Before you slate it try the formula not gn3 part try the first formula for any type B,C,D 60898 put in the parts of the formula & check it gives you the answer
you both are talking bollox, the nominal voltage hasnt changed i have bs7671:2008 inc amendment 3
check the formulae again, you should use a measured value in the formulae or your wasting your time
appendix 3 p317
for those with digital version this is the title of the section "TIME/CURRENT CHARACTERISTICS OF OVERCURRENT PROTECTIVE DEVICES AND RCDs"