I have a consumer unit with 80A 30mA RCD fitted.
It has been regularly tripping out during the day, mostly when I'm not in but with seemingly no patten.
I don't think it corresponds to any electrical load in the house, as it occurs when I'm out with not much working except for fridge / fish tank etc.

I'm not sure how to progress things, as there seems to be no patten to give me any clues.

Can anyone point me in the right direction to troubleshoot it further?
 
its most likely somthing pluged in. Remember things dont have to be switched on to be in circuit, just being pluged in is enougth for the RCD to see it.
To find the fault an Insulation Resistance tester is normally what we use. This puts a voltage through the circuit and measures the resistance to earth.
Things can then be pluged in and unpluged till the offending item is found.
If after everything is unpluged etc and a fault is still there then it will be a matter of splitting the circuit down to isolate the fault that way..
if your not gona get a sparks in at the moment. get in the habbit of unplugging everything thats not used and switch any switched spurs off to isolate as much as you can. then make a list of what was pluged in when it trips out. hopefully the list after a while will point to the offending appliance. if you still cant find it then a sparks is required
 
Last edited by a moderator:
Edd as covered virtually everything you can do yourself.

Chances are that it will be a faulty appliance, most culprits are older fridges, but as Edd said for now try and unplug things when your out, things like the TV, computers and such, as all these contribute to what is called High protective currents.

If obviously you can't track down the fault then you will need to call an electrician who will test the installation
 
Start the search on anything with filters or power supplies (pay most attention to the fridge).

Last time I had this issue it was my Cd player.
Temporarily disconnecting the earth on the player rapidly put a few hundred volts on the chassis.
The sensitivity of my equipment could not detect any current though.

Could not work out where the leak was coming from (electronics geek, but this was above me).

So put in a dedicated spur just for the Hifi bypassing the RCD.
Also put some bonding on the CD player too.

There are quite a few things I would do in my own house I would not dream of doing in a clients.

Just to really point out the obvious, what I did was dangerous, so don't do it.
 
Any outside lights spurred off sockets? They can be tinkers with rain. Last appliance I found was kettle.

Might be a dodgy RCD, get an electrician in ! Pay the money!!
 

Reply to Newbie - Advice required on RCD tripping in the Australia area at ElectriciansForums.net

Similar Threads

I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
I have a fairly recently installed consumer unit with an RCD, between it and the garden there is another, much older (25yrs?) RCB (big Wylex...
Replies
11
Views
2K
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
863

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock