I just finished the NFPA70E 2021 online training. As far as I understand it the NFPA 70E is OSHA compliant but, I feel like the guidance between them disagrees when it comes to the shock hazard of DC batteries. I work with EV type battery systems 28V to 800 V so, this is important.

OSHA general industry standard 1910.303(g)(2)(i)
"Except as elsewhere required or permitted by this standard, live parts of electric equipment operating at 50 volts or more shall be guarded against accidental contact by use of approved cabinets or other forms of approved enclosures or by any of the following means: ...."

I see no exception listed for batteries.

in the NFPA 70E 2021 training they state shock protection is not required for battery systems where you cannot reach across 100 volts of potential and this is reinforced in the Informative Annex Figure F.7 (Assessing Hazards Associated with Work on Batteries).

Am I missing something?
 
Last edited:

Reply to NFPA70E battery 100 VDC vs OSHA 50 volt standard in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock