I've been asked by a customer to remove four nights storage units and replace the switched fused spurs with single 13amp sockets.
Each unit is fed from a dedicated consumer unit supplied from a economy 7 meter.
I need to remove the meter tails from the night tariff meter and connect the consumer unit that feeds the replaced spurs through the Henley blocks that feeds the main consumer unit.
Is this practice reportable under part P and does the electrical supply companies need be informed.
 
If the off peak tariff is no longer being used I would recommend talking to the energy supplier as usually the normal tariff is more expensive when a split tariff is being used. So they may want to change the meter.

If you need to remove the tails from the off peak tariff meter this will mean cutting the seals and if they choose to change the meter they will know what you have done.

As far as Part P goes I think yes it is notifiable as it is a major modification.
 
Ist point of contact for the Customer is the Energy supplier.
They need to know and agree to drop the E7 charges.

It may be that they'll leave the existing meter in and charge the same rate for both tariffs for now, then no tail shifting required.
Or if they want to change the meter then they'll have to move the tails.
 
The householder should have a single point of isolation, the service fuse will not suffice.
 
The energy provider should do the conversion. It is their equipment, when I change from E7 to standard, e7 tails are disconnected put in blocks, meter changed to single tariff, then its over to Electrician to reconnect to 24hr supply.
 
Have not enough room to install single point isolation.
Cannot find any regulation that covers this.
Would signage surface
Reg 537.1.4, signage may apply to large commercial/industrial sites where multiple supplies are present but see no excuse on a domestic. Will the sockets have rcd protection.
 
"537.1.4 A main linked switch or linked circuit-breaker shall be provided as near as practicable to the origin of every installation as a means of switching the supply on load and as a means of isolation.
A main switch intended for operation by ordinary persons, e.g. of a household or similar installation, shall interrupt both live conductors of a single-phase supply."
 
"537.1.4 A main linked switch or linked circuit-breaker shall be provided as near as practicable to the origin of every installation as a means of switching the supply on load and as a means of isolation.
A main switch intended for operation by ordinary persons, e.g. of a household or similar installation, shall interrupt both live conductors of a single-phase supply."
Reg 537.1.4, signage may apply to large commercial/industrial sites where multiple supplies are present but see no excuse on a domestic. Will the sockets have rcd protection.
No they will not as i will not be changing the consumer unit.
The only other way i can see around this is to supply the old ecconomy 7 consumer unit from a 32 amp mcb on the main consumer unit with 6mm t&e which has a double pole switch disconnector and a 30mA rcd and this should cover all the regs?
 
You are going to have to provide additional rcd protection because you are creating new socket outlets. The best way to do this is to replace both boards with a single unit.
 
What you need to do, is get the DNO to remove the off peak meter and to have ready a dual isolator for them to connect the meter tails into.
Then you can connect both CUs into the dual isolator.
As Westward10 says, you will need to provide RCD protection for the sockets.
 
What you need to do, is get the DNO to remove the off peak meter and to have ready a dual isolator for them to connect the meter tails into.
Then you can connect both CUs into the dual isolator.
As Westward10 says, you will need to provide RCD protection for the sockets.
Problem here he is missing rcd protection with the existing board, suppose you could fit rcd sockets.
 
What you need to do, is get the DNO to remove the off peak meter and to have ready a dual isolator for them to connect the meter tails into.
Then you can connect both CUs into the dual isolator.
As Westward10 says, you will need to provide RCD protection for the sockets.
i think it would be easier if i can take the four 2.5mm t&e radial feeds from the economy 7 consumer unit and connect them to the main tariff consumer unit which has split load rcd and install 16 amp mcb for each radial circuit. this should cover all bases.
 
i think it would be easier if i can take the four 2.5mm t&e radial feeds from the economy 7 consumer unit and connect them to the main tariff consumer unit which has split load rcd and install 16 amp mcb for each radial circuit. this should cover all bases.
Yes if there are adequate spare ways.
 
"537.1.4 A main linked switch or linked circuit-breaker shall be provided as near as practicable to the origin of every installation as a means of switching the supply on load and as a means of isolation.
A main switch intended for operation by ordinary persons, e.g. of a household or similar installation, shall interrupt both live conductors of a single-phase supply."
Just a reference on this.Hello,
Please offer clarification as to whether regulation 537.1.4, or in fact any other regulation prohibits the common practice of splitting the mains supply from the meter, via Henley block to 2 or more CCU's? Each CCU in its own right has DP isolation. Does this regulation, or in fact any other regulation insist on a suitably rated DP isolator to be placed in line with the meter tails offering a single point of isolation for the 2 or more separate CCU's.

Note, an assessment of general characteristics would additionally be conducted to ensure compliance.

This question needs a written answer as evidence to address the questions within my immediate circles, that the above practice of splitting the mains supply via Henley block doesn't comply with the Regs and specifically 537.1.4.

Thank you.

Regards,


NICEIC response:

Wango
Please accept our apologies for the delay in replying to your query.
I can confirm that such practice is allowed under BS 7671. Attention should also be given to 537.2.1.3 & 537.2.2.6
I hope this helps.
Regards
**** ***** BSc MIET IEng
Area Engineer
 

Reply to night tariff meter change to standard tariff in the The Welcome Forum area at ElectriciansForums.net