Discuss No CPC in submains cable in the UK Electrical Forum area at ElectriciansForums.net

kamkam

-
Reaction score
12
Hi all just done pre site survey on a job found the following (never come across this before)

2 ccu's in the property 1 located next to the incoming head (A) and the other (B) is located approx 15 meters away

Both CCu's are feed via henley block. (A) tails are 25mm however the cable feeding (B) is 16mm 2 core non armoured double insulated PVC with no cpc. The run goes thought the fabric of the building there is no cpc run along side this cable!. There is also no isolator for that.

The cut out is 100amp the earthing arrangement is TNS.

Ze at (A) is 0.35

Ze at (B) is 0.63 (Just picking up paralel paths as there is visually no earth on that side of the building) all Zs on the (B) side are as expected very high 1.23 on sockets as an example.

The building is very old prob 200 years old with a newer extension added approx 1970's hence two dbs. The property is also in the middle of know where ie old farm house.

I want to ditch the 16mm feeding (B) and install 25mm swa via isolator etc etc. I am trying to find the reg (if it exisits) regarding the requirement of cpc in cables run though the fabric of a building so can back up my reason for running a new cable. OR would it be ok to run 16mm earth from the MET along side the current 16mm and install a fused 60amp double pole isolator. Haven't calculated VD on the 16mm yet just wanna run this by you guys for your opinion.

Let me know if I have missed any info that might help the answer...

Cheers

Kam
 
Last edited:
The reg defo exists, maybe in several parts, sorry ain't got a bgb to hand . Is the b board in the same building? I'd personally recommend pulling in an armoured. Whether you use the armour as cpc or have a dedicated core is down to you design/calculations.
 
Hi Loop3... yes the building is joined together. Seen different regs regarding cpcs but no 'one' reg that will be easy to explain the the customer (he's bit of a know it all - well thinks he is)
 
as an alternative, you could TT the sub main board, as long as all circuits are RCD protected.
 
How can it be "a very bad idea" if it's compliant??

Agreed, the ideal situation would be to extend the main earth off the existing MET to maintain TNS earthing but for cost or practical reasons, this may not always be possible. Therefore the TT suggestion which is a safe and compliant is still valid option.
 
I with E54 on this one, TTing this installation, although possible, seems bonkers in this case with a TN-S earthing arrangement in good condition only 15m away. Just export the TN-S earth by following the existing sub-main route with a 16mm[SUP]2[/SUP] earthing conductor from the MET at the origin (A) to the EMT at the sub-board (B), and fit 60A DP fused isolator at the origin (A) to supply the original sub-main.
 

Reply to No CPC in submains cable in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Been looking at a CU change in a small office and would appreciate comments on the following. Office is supplied from the mains intake in the...
Replies
52
Views
6K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
836
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hi I've got an new outbuilding that needs power run out to it, the building is very close to the house and the original plan was to run an...
Replies
9
Views
941

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock