Looking at a CU change for a young couple with kids.
There is no CPC on the lighting circuits, the cable is 2 core (red and black)
I have done a IR and continunity and all is ok, no borrowed neutrals
All the accessories are Class 2
The young couple don't have the budget to have the lighting circuits rewired.
I have got some no CPC warning lables for the CU and will state on the EIC that no CPC to lighting circuits, what readings do I put on the EIC for R1+R2 or R2?


Thanks
 
Slap a sticker on the consumer unit stating the lack of CPC on lighting circuit and that Class 1 fittings must not be used. Also ensure that back box lugs are of the insulated variety so that the 3.5mm box screws can not become live if a wire is damaged and pressed against the back box. There is also a recommendation in the ESC Best Practice Guide that a 30mA RCD should be fitted to provide additional protection. So long as you do all these things and note on any certificates that a CPC is not present then you have done as much as you can possibly do without carrying out a full rewire of the lighting circuit.
 
You could also use light switches which have plastic caps over the screws eg GET (ultimate if from TLC or wilts plus if from wilts).
 
If you can't obtain a reading that you should then it's defiantly a cross that goes in the box. so that would be a cross in ir n-e l-e. Also r1+r2, r2 and a cross in the zs box unless you state that you have carried out your zs via l-n on lighting circuits (which you will need to link out the rcd to obtain) and you will defiantly be needing to record comments on why the readings were not obtainable.Hope this helps.Carl
 

Reply to No CPC to lighting circuits in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hello everyone, I saw in the hospital every circuit has 2 separate cpc, same size, sometimes different. I'm wondering. How we can do the dead...
Replies
1
Views
882
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
800
I've tried to research and form a plan without asking on here, but I'm just going around in circles. Just completed an EICR. The wiring ranges...
Replies
15
Views
2K
I have a light switch where the CPC has been used for a lighting circuit and sleeved. Previously I would give this a C3 (411.3.1.1) and leave a...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock