Discuss No earth in garage - should I be worried? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
3
Hi,

We recently moved into a new house about 6 months ago and all of the plug socket wiring seems to have the standard, live, neutral and earth wiring as one would expect. However, go out into the garage (separated from the house) and it appears to only have Live and Neutral wiring (old style red and black respectively).

I only found this out recently after changing the facia and backbox to a plastic one as the old one was metal and rusted only to find 2 wires.

My question is, should I be worried and should I get an electrician to come out and quote to rewrite the garage? It seems like a big job as it looks like the wiring goes under ground potentially and is concreted in.

Thanks for any advice.
 
Here are some photos of the wiring and the socket/light switch. I have disconnected them as I didn't think they were safe, but this is essentially the wiring inside and it doesn't have an earth.

20181221_154021.jpg


20181221_154026.jpg


20181221_154032.jpg
 
Those cables are MICC (mineral insulated copper conductors) and the copper sheath is the earth provided it is correctly connected at all points of termination. You are correct the existing accessories are corroded which is likely to affect earth continuity of the cables. As it stands you need to replace them with metal accessories to maintain the earth, with separate earth protective conductors from front plates to back boxes of the accessories. I would recommend getting an experienced electrician in as those cable glands require correct connection and retesting.
 
So, old house but new to you. That nipple switch must be a good few years old (the analysts will call it a toggle switch)
 
Those cables are MICC (mineral insulated copper conductors) and the copper sheath is the earth provided it is correctly connected at all points of termination. You are correct the existing accessories are corroded which is likely to affect earth continuity of the cables. As it stands you need to replace them with metal accessories to maintain the earth, with separate earth protective conductors from front plates to back boxes of the accessories. I would recommend getting an experienced electrician in as those cable glands require correct connection and retesting.
Nice one, as they where so blackened I didn't notice, must be a lot of damp in the place.
 
It looks like the sockets are installed using MICC or Mineral Insulated Copper Sheathed cable, whereby the Copper sheath was is acting as the cpc (Earthwire)

However if you say you took the socket away from the box and there was no earthwire, the socket would have been earthed, but as soon as you removed it from the back box there would be no earth on the faceplate, the Electrician should have provided a fly lead from the back box to the socket.
You will be hard pressed to swap the back box with this type of installation, as disturbing any MICC cables is fraught with dangers unless you have experience of this type of cable.
If you are still intent on swapping the sockets and back box, then consult an Electrician to do the work for you, he can swap both the back box and socket with a nice new shiny one, shouldn't be that expensive, of course that depends on how many you want changing, sorry for the long post. Good luck, post your postal area and a member may live close to you and may offer to do the work, for a price of course.
 
Or replace with a Crabtree metal box or terminate the MICC to a metal box that then feeds a socket, either way best to get an electrician in.
 
Piranha nut springs to mind.
Don't suppose they had heard of those things back when that install was done, earthing was provided by proper installation methods and good workmanship, there ought to have been a lead from the backbox to the Earth Terminal on the socket faceplate, but should the OP decide to employ an Electrician to swap the sockets and backbox the a Piranha washer would be a good addition, along with a fly lead from Box to socket.
 
Ok thanks for the advice. Imagine they are going to laugh at me for replacing another socket in there with a plastic one then...my postcode is ****** if anyone is available to come and quote. Thanks.
 
Last edited by a moderator:
Don't suppose they had heard of those things back when that install was done, earthing was provided by proper installation methods and good workmanship, there ought to have been a lead from the backbox to the Earth Terminal on the socket faceplate, but should the OP decide to employ an Electrician to swap the sockets and backbox the a Piranha washer would be a good addition, along with a fly lead from Box to socket.
3/4 Piranha nut, good luck with that:D
 
Don't suppose they had heard of those things back when that install was done, earthing was provided by proper installation methods and good workmanship, there ought to have been a lead from the backbox to the Earth Terminal on the socket faceplate, but should the OP decide to employ an Electrician to swap the sockets and backbox the a Piranha washer would be a good addition, along with a fly lead from Box to socket.
This is for "now" my workmanship on MICC was 100% and I always was volunteered for the "awkward" jobs, if there was a specialist area or an additional earth was required then you used a sealing pot with an earth tail.
Screenshot 2018-12-21 at 16.27.13.jpg
 
3/4 Piranha nut, good luck with that:D
Wasn't thinking meant to say use a serrated washer, that would improve the connectivity for earthing the MICC, of course you are correct a Piranha nut would be difficult to adapt, a serrated washer would be my first choice along with a fly lead from box to socket.
 
I hope our Chris doesn't rip out the MICC.
He just needs a can or two of this to make it look fantastic. Give him something to do whilst he's waiting for someone to come and check it out.

1141040-1.jpg
 
I hope our Chris doesn't rip out the MICC.
He just needs a can or two of this to make it look fantastic. Give him something to do whilst he's waiting for someone to come and check it out.

1141040-1.jpg
Chris PM me your address I'll check out the distances, after Christmas though
 
Haha no chance I'm buffing that thing up! Yeah ****** is the postcode. Sounds like you guys know your stuff so would rather have a specialist. But understand if it's too far. Will p.m. you my number.
 
Last edited by a moderator:
if the incoming MICC tests OK. it could be terminated into an adaptable box, then the garage rewired in alternative cable.
 
It looks like damp in the air and penitration (easy SWD)of water through the single skin of brickwork I don't think todays M/Clad will last so long.If the R2 proves to be ok might need cleaning up and a inperial to metric to adapt for earth nut to a basic IP socket.
 
Ok so here is what I have done as a temporary solution on the other socket that I replaced with plastic (the green wire is dead as it feeds from downstairs which is disconnected). I know it's not ideal but it really is temporary - at least it has an earth now?

Thanks for your help so far.

p.s. be nice, i'm no electrician - it's temporary until I can get one out.

20181222_085946.jpg
 
Ok so here is what I have done as a temporary solution on the other socket that I replaced with plastic (the green wire is dead as it feeds from downstairs which is disconnected). I know it's not ideal but it really is temporary - at least it has an earth now?

Thanks for your help so far.

p.s. be nice, i'm no electrician - it's temporary until I can get one out.

View attachment 46611
Very dangerous piece of work, don't even think of using it, isolate it and get an electrician in PDQ that is naughty, seriously don't use it. If that is on the same circuit as the others you want changing, switch it OFF and wait for help. That's not a solution.
 
Ok so here is what I have done as a temporary solution on the other socket that I replaced with plastic (the green wire is dead as it feeds from downstairs which is disconnected). I know it's not ideal but it really is temporary - at least it has an earth now?

Thanks for your help so far.

p.s. be nice, i'm no electrician - it's temporary until I can get one out.

View attachment 46611
are you Romanian?
 
I am a bit confused on the set up you described you say a garage away from the house then say regarding this cable the green cable. What you have done thereby removing the pot and gland and pushing sleaving down is making a deteriorated installation into a potentially dangerous one the socket tester only tells you that this is wired correctly it does not tell if the earth wrapped around the copper sheath is sound enough to give you a good enough low resistance that under a fault can blow or trip the protective device. The supply for the garage from the house is it RCD/RCBO protected (maybe a photo).
 
Ok so here is what I have done as a temporary solution on the other socket that I replaced with plastic (the green wire is dead as it feeds from downstairs which is disconnected). I know it's not ideal but it really is temporary - at least it has an earth now?

Thanks for your help so far.

p.s. be nice, i'm no electrician - it's temporary until I can get one out.

View attachment 46611
please get a spark in to rectify the situation. that is beyond words. even a plumber could do better ( unless he works for British Gas).
 
Ok so here is what I have done as a temporary solution on the other socket that I replaced with plastic (the green wire is dead as it feeds from downstairs which is disconnected). I know it's not ideal but it really is temporary - at least it has an earth now?

Thanks for your help so far.

p.s. be nice, i'm no electrician - it's temporary until I can get one out.

View attachment 46611

What could possibly go wrong!
 

Reply to No earth in garage - should I be worried? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, I own a country Villa out in the Spain countryside. Was having problems with water pressure so local tradesmen advised to get a water...
Replies
14
Views
1K
I want to make some electrical upgrades to my detached garage. I want to update the subpanel in the detached garage, and I want to add a 240V...
Replies
3
Views
754
can anyone please advise on where the wires go? My electrician installed a new cable ready for when I bought a security light. The cable as shown...
Replies
3
Views
627
Hi all, I’ve purchased a Ring Spotlight camera and decided to remove the old spotlight that’s currently installed on the house we recently...
Replies
2
Views
285
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
914

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock