Discuss No end to end 2 Radials on one MCB in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Hello, I have tried to search the forum but have not found anything although this must have been asked a thousand times.

When completing a board change for example and there is no end to end on the neutral does downgrading the mcb to a 20amp and effectively running two radials from the same MCB comply with BS7671 ?

End to end on r1 and r2 are good (I just can not for the life of me find the break in rn, other than to identify its likely under the floor under some nice new tiles)

Im happy to do some reading if someone could point me to the correct chapter in the book.

And if this is ok (2 radials from one MCB) having taken into account demand, how would the results be recorded on the schedule ?
 
Hello, I have tried to search the forum but have not found anything although this must have been asked a thousand times.

When completing a board change for example and there is no end to end on the neutral does downgrading the mcb to a 20amp and effectively running two radials from the same MCB comply with BS7671 ?

End to end on r1 and r2 are good (I just can not for the life of me find the break in rn, other than to identify its likely under the floor under some nice new tiles)

Im happy to do some reading if someone could point me to the correct chapter in the book.

And if this is ok (2 radials from one MCB) having taken into account demand, how would the results be recorded on the schedule ?
Read the definition of a Circuit in BS7671 "Definitions" page 24
"Circuit" An assembly of electrical equipment supplied from the same origin and protected against overcurrent by the same protective device(s)
 
New board change I would make separate radials from them over separate protective devices.
[automerge]1570631647[/automerge]
I would personally be looking to eliminate the section of cable with the broken neutral completely. Sometimes however this can leave an unfortunate split of the outlets whereby if you have ten points one radial may include nine of them.
 
Last edited:
Read the definition of a Circuit in BS7671 "Definitions" page 24
"Circuit" An assembly of electrical equipment supplied from the same origin and protected against overcurrent by the same protective device(s)


so my interpretation, an assembly of electrical equipment (accessories on 2 radials) supplied from the same origin (DB at origin) and protected against overload protection by the same protective device (s) (MCB at DB)

So yes 2 radials from one MCB is by the letter of the law one circuit ?.

And having 2 radials from one MCB is not in contravention of BS7671 ?
 
That is debatable. If you are putting a new board in eliminate the faulty section of cable and split onto two 20A devices. Why leave a broken connection in situ.
 
That is debatable. If you are putting a new board in eliminate the faulty section of cable and split onto two 20A devices. Why leave a broken connection in situ.
I agree very debatable, and lots will have different opinions. I suppose what I want to try and find out is does BS7671 forbid the use of 2 radials in one MCB. If so whats the reg number ?
 
Are you going to eliminate the faulty section creating two separate radials?
I side with Regulation 314.4 whereby each final circuit which each radial is shall be connected to a separate way in a distribution board, this is Division of Installation. Others argue the days away with the definition of a circuit as opposed to final circuit which this Regulation refers to, each to their own.
 
Last edited:
so my interpretation, an assembly of electrical equipment (accessories on 2 radials) supplied from the same origin (DB at origin) and protected against overload protection by the same protective device (s) (MCB at DB)

So yes 2 radials from one MCB is by the letter of the law one circuit ?.

And having 2 radials from one MCB is not in contravention of BS7671 ?
Not really the right way to install two radials, but as far as 7671 is concerned no it isn't but doing it from scratch, two separate ciricuits will be the best way, have a look at Appendix 15 in BS7671 for details on RFCs and radial circuits.
 
Are you going to eliminate the faulty section creating two separate radials?
I side with Regulation 314.4 whereby each final circuit which each radial is shall be connected to a separate way in a distribution board, this is Division of Installation. Others argue the days away with the definition of a circuit as opposed to final circuit which this Regulation refers to, each to their own.
Absolutely
Are you going to eliminate the faulty section creating two separate radials?
I side with Regulation 314.4 whereby each final circuit which each radial is shall be connected to a separate way in a distribution board, this is Division of Installation. Others argue the days away with the definition of a circuit as opposed to final circuit which this Regulation refers to, each to their own.
yes, will eliminate faulty section
 
n
I see no point in connecting them to the same protective device.
No I agree but running out of space on the board, already added a new circuit which has taken last MCB. Just wanting to check that when Im signing the eic (and the two radials are in the same MCB) the work completed by my complies with BS7671.

I know I should have planned for leaving a couple of spare ways !
 
There is nothing wrong in using multiple cables in one termination provided that terminal is designed for that purpose and you are not using the terminal past its capabilities.

The circuit was on one protective device before so I see no reason why it can't go back onto one as two legs of a radial.

It would be best to divide them up if possible but not essential.

As mentioned, the most important thing is that you disconnect the faulty leg of cable and make safe the ends. This usually means connecting them to the installation earth.
 
Can you not fault find the cable run with the break / open circuit and pull a new leg in to reform the ring?
 
Can you not fault find the cable run with the break / open circuit and pull a new leg in to reform the ring?
Could be just a bad connection at one of the accessories.
 
Hello, I have tried to search the forum but have not found anything although this must have been asked a thousand times.

When completing a board change for example and there is no end to end on the neutral does downgrading the mcb to a 20amp and effectively running two radials from the same MCB comply with BS7671 ?

End to end on r1 and r2 are good (I just can not for the life of me find the break in rn, other than to identify its likely under the floor under some nice new tiles)

Im happy to do some reading if someone could point me to the correct chapter in the book.

And if this is ok (2 radials from one MCB) having taken into account demand, how would the results be recorded on the schedule ?
Is the area covered by the 2.5mm radials greater than 50 square meters ?
 
I am having the same problem, I have open circuit on neutrals. Upstairs is all laminate flooring. I believe the problems is lying in an inaccessible JB underfloor boards upstairs. Can anyone give me a technique I can check this before having to rip up flooring upstairs. I tried splitting ring to how I would expect it to be run, I then continuity tested 2 legs which I believed would be the faulty cable, disconnected it. Turned out I then had no sockets with power in kitchen ?
 
I am having the same problem, I have open circuit on neutrals. Upstairs is all laminate flooring. I believe the problems is lying in an inaccessible JB underfloor boards upstairs. Can anyone give me a technique I can check this before having to rip up flooring upstairs. I tried splitting ring to how I would expect it to be run, I then continuity tested 2 legs which I believed would be the faulty cable, disconnected it. Turned out I then had no sockets with power in kitchen ?
Sometimes you have to split the whole thing down and through continuity testing make a map of where each portion of cable goes to. Then you can figure out where likely locations of hidden joints might be and parts that may be spurred from other parts etc.
 

Reply to No end to end 2 Radials on one MCB in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, Had a weird one this morning during an EICR. Testing a ring final circuit in a 2 bed flat… kitchen was on a separate ring. With only the...
Replies
7
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
For example the house today had two lighting T&E in the same MCB. I know it's fine, but as I test both 'radials' where and how do we enter them on...
Replies
6
Views
838
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
hi in college and watched some YouTube videos and read up on things I think I got the right formula but I'm not sure. Zsc= Zesc(or Zdbsc) +...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock