Discuss No Main Earthing Condictor or Ze in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Marcus Vaughan

-
Esteemed
Reaction score
240
This has thrown me - obviously wet behind the ears.

A customer has asked me to carry out an EICR - but when I get there - it seems one has been done already....

It states 'no earth, no RCD'. Sure enough when I looked around there was a new service head from the DNO-very long tails?..

And no earthing conductor - as in no Ze......

So I phone the DNO - they say that yes they have not provided an earth - yes that they can provide one (TNCS). That I get....

But then they say you can just install an RCD main switch? That's what's thrown me - I know you can/should do that for TT systems - but that's based on some sort of earth electrode somewhere.

I can't find one?

Is this a case of install earthing electrode and RCD or get DNO to provide an MET?
 
It's a case of both.
Knock in a rod and use an upfront RCD as a temp measure until the DNO provide their earth connection.

If the customer does not want the temp work done get them to sign a danger notification to cover yourself.
 
But then they say you can just install an RCD main switch?

a case of some muppet at DNO talking through his arse. an RCD should never be used as a substitute for an earthing system. only as a back-up with a high Ze on a TT.
 
my understanding is the dno does not have to provide an earth, if however they do supply one , then they have to maintain the earth. like wise a alteration such as a new service head then after it should not be left in any worse situation than before. so if they changed the service head and previously there was a earth connection and now they have left it without one then you arguably can force them to make it safe. be that provide an earth connection or install a tt rod. it should not come down to the homeowner to get an electrician in as the dno have in effect made the system unsafe. im sure somewhere in the various laws there will be something about this.
 
bY THE BYE gAVIN, CAN I JUST BRING YOU TO TASK ON YOUR GRAMMAR. :)
@Midwest point taken, My grammar is sometimes good sometimes bad, depends if i am tired and typing the way i think things in my head.. being a country bumpkin from Somerset just being able to speak English coherently is a sign of intelligence. writing and grammar, well that is a bonus...
 

Reply to No Main Earthing Condictor or Ze in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
1K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
859
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Fluke MultiFunction Tester 1662 TNS Earthing system. Switchboard - 415v - 3 Phase + Neutral + Earth. MCB 1000A 3 individual Earths (185mm)...
Replies
22
Views
3K
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock