pre cut out break in neutral could lead to harmful voltage on casings of class I equipment,this could be touched at same time as pipes/metal if they are at earth potential-extreaneous
 
Its purpose is to keep all conductive exposed parts at the "SAME" potential or as close to it as possible so as its bonded to earth if it has a potential because of a fault the earth in the zone should be at the same or close to the potential so reduce or eliminate the risk of a shock.
In layman terms without it a fault could make the pipes live resulting in an electric shock.
 
In addition to post #3: if they are extraneous, then for the duration of an earth fault (short circuit to earth) - which could be up to 5 seconds for a distribution circuit (or a final circuit over 32A) - the exposed-conductive-parts (bits of metal that are part of your electrical installation, like the casing of class 1 equipment) will be at a different voltage to extraneous-conductive-parts (your water/gas pipes) which is a shock risk.

If RCDs for additional protection are present, the risk associated with the above is significantly reduced... in practice, the RCD will almost certainly trip and clear the fault a lot faster than the OCPD.
 
Its purpose is to keep all conductive exposed parts at the "SAME" potential or as close to it as possible so as its bonded to earth if it has a potential because of a fault the earth in the zone should be at the same or close to the potential so reduce or eliminate the risk of a shock.
In layman terms without it a fault could make the pipes live resulting in an electric shock.

This is incorrect and misleading. The sole purpose of main bonding is to prevent a rise in voltage on conductive parts (read the definition of a conductive part) during a fault, resulting in a shock risk to a person in simultaneous contact with a metallic service introducing the general mass of earth into the property. It's nothing to do with pipes becoming live.
 
Its purpose is to keep all conductive exposed parts at the "SAME" potential or as close to it as possible so as its bonded to earth if it has a potential because of a fault the earth in the zone should be at the same or close to the potential so reduce or eliminate the risk of a shock.
In layman terms without it a fault could make the pipes live resulting in an electric shock.

This is incorrect and misleading. The sole purpose of main bonding is to prevent a rise in voltage on conductive parts (read the definition of a conductive part) during a fault, resulting in a shock risk to a person in simultaneous contact with a metallic service introducing the general mass of earth into the property. It's nothing to do with pipes becoming live.

Arnt you both saying the same thing?
 
This is incorrect and misleading. The sole purpose of main bonding is to prevent a rise in voltage on conductive parts (read the definition of a conductive part) during a fault, resulting in a shock risk to a person in simultaneous contact with a metallic service introducing the general mass of earth into the property. It's nothing to do with pipes becoming live.

I dont understand I am misleading and you arnt yet we are singing from the same hymn sheet is a pipe that should be bonded not a conductive part? I didnt quote rules or regulations I said it in laymans terms as asked.
 
All right you have to join the main water and gas pipes with a bit of 10mm earth cable to ensure they are at the same potential as earth.
 
This is incorrect and misleading. The sole purpose of main bonding is to prevent a rise in voltage on conductive parts (read the definition of a conductive part) during a fault, resulting in a shock risk to a person in simultaneous contact with a metallic service introducing the general mass of earth into the property. It's nothing to do with pipes becoming live.

I think he means the pipe would rise to the same potential.
 
I dont understand I am misleading and you arnt yet we are singing from the same hymn sheet is a pipe that should be bonded not a conductive part? I didnt quote rules or regulations I said it in laymans terms as asked.

But it's wrong.
A pipe is not a conductive part,a conductive part is a metallic part of the electrical installation which would not normally be live but which may become so under fault conditions. A metallic non electrical service coming into a building from externally is likely to be at earth potential by virtue of being in contact with the general mass of earth,and will remain at earth potential if it is not connected to conductive parts. Explain how a pipe will become live if it is not bonded? If you are going to explain something in laymans terms at least get it right.
 
Last edited by a moderator:
It may be at earth potential but is it equipotential to the rest of the earthed metalic electrical instalation. It needs to be kept equipotential in case a fault occurs on an immersion heater etc. Hence they need to be joined.
 
But it's wrong.
A pipe is not a conductive part,a conductive part is a metallic part of the electrical installation which would not normally be live but which may become so under fault conditions. A metallic non electrical service coming into a building from externally is likely to be at earth potential by virtue of being in contact with the general mass of earth,and will remain at earth potential if it is not connected to conductive parts. Explain how a pipe will become live if it is not bonded? If you are going to explain something in laymans terms at least get it right.

You are missing the word 'exposed'. You mean to say 'an exposed conductive part'.
 
It may be at earth potential but is it equipotential to the rest of the earthed metalic electrical instalation. It needs to be kept equipotential in case a fault occurs on an immersion heater etc. Hence they need to be joined.

But how does it 'become live' if it's not bonded?
 
Last edited by a moderator:
Unbelievable.
And you claim to be an electrical engineer?

So you think all earths are at the same potential then so you will never get a potential between 2 earth rods spaced apart or a rod and a pipe in the ground at the front and rear of the property.

Dont want to fight would discuss seems if you dont agree, you question who or what I am either discuss with facts or I will ignore you
 

Reply to No main equipotential bonds in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I have a customer who is looking to replace their electric shower. There is equipotential bonding connected to the cold feed. I’ve not seen...
Replies
11
Views
869
Hi forum members, I hope someone can assist with my enquiry. I have been advised that to comply with BS7671 Reg 132.16 my solar and battery...
Replies
5
Views
2K
Hi I have a 1st fix domestic install on the go and need to leave a socket for other trades to use after me. There is no main bonding at the...
Replies
7
Views
832
Not sure on this one. Mains water is coming up from the ground in lead pipe in bathroom. 2 inches of copper pipe before the stop tap. All...
Replies
4
Views
1K
Just a thought guys in terms of RCBO’s and supplementary bonding. Obviously supplementary bonding isn’t required as long as a 17th / 18th...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock