Discuss No neutral on three phase in the UK Electrical Forum area at ElectriciansForums.net

magnoliafan89

-
Esteemed
Arms
Reaction score
540
Hi all
Need some help remembering some college work.
Been doing a job and we are pulling in 400mm singles in parallel, got three phases and a seperate earth but no neutral.
From what i remember from college was it becuase if you had the phases all balanced youd have no current to go on a neutral so dont need one. I was trying to remember all those calculations and diagrams we did in college so i asked the bloke i was with to explain it to me so i could better understand but he said he couldn't remember either.
Is this why there is no neutral and it is as simple as the loads being balanced or was there another reason?

Thanks for any help guys hope you're all keeping busy
 
Hi all
Need some help remembering some college work.
Been doing a job and we are pulling in 400mm singles in parallel, got three phases and a seperate earth but no neutral.
From what i remember from college was it becuase if you had the phases all balanced youd have no current to go on a neutral so dont need one. I was trying to remember all those calculations and diagrams we did in college so i asked the bloke i was with to explain it to me so i could better understand but he said he couldn't remember either.
Is this why there is no neutral and it is as simple as the loads being balanced or was there another reason?

Thanks for any help guys hope you're all keeping busy
What Voltage are the single operating at LV or HV and what are they feeding?
Comparison between Star and Delta Connections - Electrical Technology - https://www.electricaltechnology.org/2014/09/comparison-between-star-and-delta-connections.html
 
If its coming from lv side of transformer to feed a switchboard i would have thought it would need a neutral because the star point connection would be at the transformer winding
 
If its coming from lv side of transformer to feed a switchboard i would have thought it would need a neutral because the star point connection would be at the transformer winding
That's right who's idea was it to run just the 3 phases, this doesn't have anything to do with a wind generation install does it?
 
You don't need a neutral for:

a) 3-phase loads that are delta connected, regardless of whether they are balanced or not. All current is taken between the lines and there is no neutral point to connect. Line currents may be equal e.g. motors, or different e.g. machinery with a delta-star input transformer.

b) 3-phase loads that are star-connected, provided they are inherently balanced. E.g. 400V 3-phase heater battery with 230V elements, the star point will sit near neutral volts and it doesn't matter if it strays a little due to differences in resistance, so there's no need to actually connect it to supply N. Line currents will be equal.

c) Single-phase loads operating at line-line voltage. E.g. some welders, control transformers in 400V machinery. Again no neutral connection on the device as the current is taken between two lines. Often referred to as 2-phase loads (because they connect to two phases) but technically single-phase.

A machine with a mainly balanced load (e.g. 40kW of 3-phase motors, 250W of single-phase 230V computer) will often have a 400-230V stepdown transformer to supply all single-phase loads line-line to avoid the need for a neutral connection.
 
Hi guys thanks for the answers sorry i haven't replied its been a long day. They are being fed off a 11kv sub which is obviously stepped down to then feed the switch they come from and its feeding a machine the other end.
Again thanks for the responses guys :)
 
A machine that supposedly melts plastic.
Not much known about it, then?
Some form of extruder.....may be melting plastic for remoulding purposes? You don't just melt plastics, it's for a reason.
Still, with such a supply, it'll be big....if it's specifically for that purpose.
In such cases, though, it would have to be assumed that other local machines would be involved....for remoulding, at least.
 
Not much known about it, then?
Some form of extruder.....may be melting plastic for remoulding purposes? You don't just melt plastics, it's for a reason.
Still, with such a supply, it'll be big....if it's specifically for that purpose.
In such cases, though, it would have to be assumed that other local machines would be involved....for remoulding, at least.
Yeh an extruder. I dont know much about the machine ive just seen the plans and came up midway through the job
 

Reply to No neutral on three phase in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
843
I’m just finishing my L2 2365 at college in the evenings and plan to do the L3 2365 with the same college as an evening course. However I would...
Replies
0
Views
260
Hello all, I signed up here for a little help. I bought a 3 phase bandsaw and went down the rabbit hole of VFD’s etc. ‘The motor is 3 phase 400v...
Replies
9
Views
1K
Hi All, From what I understand, working out the design current - Ib for single phase is quite easy (max appliance power/voltage). For three...
Replies
7
Views
2K
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
999

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock