Simon_

Fitted 2 new rings and a new CCU. Got readings on r1 r2 rn end to end on both and also R1 R2 R1 RN on both but no rn on downstairs ring, it just shows open circuit. Checked all sockets for loose wiring but all ok. Any suggestions? Thanks
 
I dont understand as you say you tested end to end rn on both circuits which was OK.

As Mayfair has said you have a open circuit in the neautral if you have no end to end rn.

Split the circuit at the CU and test each leg of the neutraluntil you find the break. With a new circuit which you have just put in should be easy.
 
Fitted 2 new rings and a new CCU. Got readings on r1 r2 rn end to end on both and also R1 R2 R1 RN on both but no rn on downstairs ring, it just shows open circuit. Checked all sockets for loose wiring but all ok. Any suggestions? Thanks

Not wishing to be picky but what you've outlined doesn't make sense
 
split ring at CU. wander lead connected to 1 neutral at C. follow sockets with wander lead, break out box, and meter on the N till you lose it. iif you ain't got a wander lead. get a plug top, short N to E then with meter on buzzer at the cu across N and E, plug in sockets till you get no buzz. you have then just passed the break.
 
Last edited:
split ring at CU. wander lead connected to 1 neutral at C. follow sockets with wander lead, break out box, and meter on the N till you lose it. iif you ain't got a wander lead. get a plug top, short N to E then with meter on buzzer at the cu across N and E, plug in sockets till you get no buzz. you have then just passed the break.

You should market a set of plug tops for this tel, you'd probably make a mint this day in age
 

Reply to No rn reading on downstairs ring in the Australia area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hello all. So I am sure the expertise on this forum will be able to decode this very easily. But it has completely baffled me. I'm in training so...
Replies
14
Views
608
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
Hey there, Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52. My question is I had a fault...
Replies
4
Views
1K
Hi so i am doing a test on sockets on a ring Final circuit for family member. Got my end to ends r1 0.62, rn 0.64, r2 0.97, identified opposite...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock