Discuss Not enough amps maybe????and Rcd tripping in the Australia area at ElectriciansForums.net

F

Firebucket

Morning sparkies:)
Was on a job when his neighbour asked if i could have a quick look at his place, as his power trips of all the time? And his bills have gone up dramatically. Has a home energy meter that tells him he's using power even with every thing off???

5 bed 15 years old no paperwork? SWA to garage but looks like T&E 10mm to shed, shed, shed & somerhouse
It's TN-C-S single phase 100A cutout / meter, 16mm to MET incoming

into connectors (sorry forgot propper name) then split to

DB1 main switch rcd 100A
2 X mcb 40A mira 9Kw shower, then 4 X mcb 32 all rings for Bedrooms, kitchen,lounge, landing,
nothing excessive two Dble sockets per B'room , single oven, couple of computers.

DB2 main 100A Dble pole switch
mcb 20A cooker, mcb 32A 2 13a sockets?, 8 X mcb 6A controlling the lights althought only normal numbers of pendants, RCBO 32A to garage in SWA, RCBO 32A controlling one of the sheds?

Each shed has it's owne DB but they are all in poor condition???!!!

Took a Zs in kitchen 0.54 and 0.43 in lounge both times tripping the RDC (on none trip?)
Zs in last shed (through 3 Db's not rcd protected) was 1.16

It trips regularly but not at or on any perticular socket/ring/time

First step I guess when I go back (paid visit) is take a ZE and get some Zs's as may be all the circuits are leaking making the rcd trip at anything.
The other concern (and sorry to sound dum to the old hands here I'm newish to this lot) Is having DB1 and DB2 with so many ways and not much loading on each, could this be some of the problem?

So knowlegable people considering the lights physically dim when the showers are run where the hell should I start with this mess

Thanks in advance and again sorry for sounding dum (been hiding behind minor works jobs since leaving college!)

Cheers Duncan
 
Yes also agree a PIR would be the way to go.

Also test the main RCD on DB1 with no load connected and also ramp test. Ramp test again after powering up 1 circuit at a time with equipment connected and see if readings vary. Could be an accumulation of earth leakage on the connected equipment.
 
Last edited:
Been out today

couldn't get RCD to trip (it was actually a 100A 30Ma) So ramp tested it on it's own, still no joy, Ok so popped in a new one and no trouble on it's own but wouldn't work with all the circuits back in/on, eliminated them all (as they gave good'ish results) bar the kitchen ring. unplugged every thing on the ring and bingo all fine and dandy, turned out to be the Fridge Freezer as well as the old rcd. Did a ring final just to make sure and left with a happy customer,

And more work to come as they want all the shed's power sorting properly:D

Cheers

Duncan
 
Last edited by a moderator:

Reply to Not enough amps maybe????and Rcd tripping in the Australia area at ElectriciansForums.net

Similar Threads

An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Conversation developed with a middle aged lady who has recently lost her husband. Note to self, stop walking dog around the graveyard Anyway...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock